If you have a fuel use load calc that indicates a heat load in the 36,000 BTUhr range there's really little point to doing a Manual-J as well.
Even the smallest mod-cons out there will cover that load, very few cast iron boilers that wouldn't either. Any 50K (input or output) boiler covers your design temp load with margin. With your load and radiation any one of the following would be a better choice than any cast iron beast, and may even be cheaper to install:
Boiler Model Minimum input Maximum input
NTI Trinity TX51 7100 BTU/hr 57,000 BTU/hr
Navien NHB80 8000 BTU/hr 80,000 BTU/hr
HTP UFT-80W 8000 BTU/hr 80,000 BTU/hr
Lochinvar CDN040 9000 BTU/hr 40,000 BTU/hr
Despite the stubby radiation of your six micro- zones the overlap of calls for heat would be high with any of the above if you dialed them in. With a total of 185' of baseboard and a 36,000 BTU/hr load you would be able to run in mid-90s combustion efficiency even under outside design conditions. If any two zones are calling for heat there is sufficient baseboard to balance with the minimum output of the above boilers.
With a non-modulating cast iron boiler (even if right-sized for the whole house load) you would be short cycling the thing on zone calls unless you combined zones unless you combine some zones. If you insist on cast iron about the best you'll do for right-sizing is the
W-M CGi 2.5. But the 42,000 BTU/hr of 190F output needs a minimum of 70' of baseboard running to not cycle at all, and at least 50' to be able to keep it from short cycling. With a bigger boiler than that the cycling problem grows. None of your zones are sufficient on their own:
From your other thread you have:
- Zone 1 - Downstairs office one, bath & hall (640 sq. ft), baseboard 24 lineal feet
- Zone 2. - Downstairs office two (504 sq. ft), baseboard 38 lineal feet
- Zone 3 – Upstairs Master BR & Bath, baseboard 25 lineal feet
- Zone 4 - Upstairs LR, DR, Main Bath, & Kitchen baseboard 42 lineal feet
- Zone 5 - Upstairs bedrooms 2 & 3, baseboard 28 lineal feet
- Zone 6 – Future expansion to unheated loft/attic, projected baseboard 28 lineal feet