Before I glue everything together...is a 90 Elbow below grade acceptable for a dry vent?
MikeGA
North Jersey
Title says it all... I've always assumed that only 45s can be used below ground for venting. Can I use this street 90 that will tie into a dry vent going straight to through the roof?
wwhitney
Berkeley, CA
Your dry vent need to come off vertical and stay vertical until at least 6" above the fixture flood rim. Here vertical means at least 45 degrees above level.
So no horizontal dry vents under the slab.
Cheers, Wayne
MikeGA
North Jersey
Cheers, Wayne
I don't understand how I accomplished that, if I need to angle it somehow.
wwhitney
Berkeley, CA
Generally the way you accomplish that is that you arrange for your drain that needs a dry vent takeoff (e.g. the shower) to pass under wall framing where the vent takeoff can occur. Then you just takeoff straight up and go up into the wall.
Or you can arrange for the drain to run parallel to and just next to the wall. Then the vent can come off at 45 degree from plumb, leaning towards the wall, so that the vent will pass under the wall before rising above the slab. Then with a 45 it turns straight up into the wall.
Or you use wet venting via the lav drain, so that you don't have to have dry vent takeoffs below the slab.
If you provide a labeled picture or scaled floor plan of the full bathroom, including wall locations where a dry vent could be run, along with the fixture locations and where you need to tie in to the building drain, then we could advise you on those options.
Cheers, Wayne
Weekend Handyman
Active Member
Nova Scotia
I am not a pro. If you can upload a diagram of what you are trying to achieve, folks might be able to give you some suggestions.
MikeGA
North Jersey
Cheers, Wayne
MikeGA
North Jersey
Does this explain what I'm trying to accomplish?
wwhitney
Berkeley, CA
The red text over the soil is too small to read, other than the part about the 30" vanity.
But based on the layout, and assuming you don't plan a wall between the WC and shower (you could have a partial wall, it would just take up more thickness than only glass), then the options I see are shown in blue and green. Two different options, pipe size is not shown, but the shower drain is 2" and the WC drain is 3", with the vent 2" or 1-1/2" depending on your plumbing code. NJ uses the NSPC, which is different from the IPC and UPC, so I forget what size they require for a WC vent. The shower wet vents the WC.
The lav would need its only dry vent takeoff, and then both dry vents need to ultimately go to the roof. They can tie into existing dry vents, at least 6" above the flood rim of all the associated fixtures. Or if NJ allows AAV you could use 1 or 2 AAVs for venting.
Cheers, Wayne
MikeGA
North Jersey
Cheers, Wayne
Black Circle =Closet flange for toilet (12.5” off stud & 15” off end of shower pan)
4" Main Drain = This isn't a vent that goes through the roof, it ties into the toilet from upstairs, which has a separate dry vent that I will tie into.
Maymay6
Georgia
If you provide a labeled picture or scaled floor plan of the full bathroom, including wall locations where a dry vent could be run, along with the fixture locations glue gorilla glue reviews and where you need to tie in to the building drain, then we could advise you on those options.
Cheers, Wayne
Except for the portion referring to the 30" vanity, the red lettering above the soil is too small to see.
However, given the arrangement and presuming there won't be a wall between the toilet and shower (you could have one, but it would add thickness beyond just glass), the alternatives I can see are those in blue and green.
There are two alternatives, the pipe size is not depicted, but the shower drain is 2 inches, the WC drain is 3 inches, and the vent is either 2 inches or 1-1/2 inches depending on your local plumbing code.
I don't remember what size is required for a WC vent in NJ because they use the NSPC, which is different from the IPC and UPC.
The toilet becomes moist from the shower.