So, one thing led to another and I now find myself needing to correct a drainage/venting problem.
The Situation
This matter involves a long and narrow (IOW tiny!) 3/4 bath (8' x 4') located on the ground floor above a crawlspace in one-half of a side-by-side/townhouse-style two-story duplex. As shown below, the original toilet only provided ~14" of clearance in front of the bowl - IOW from the nose of the bowl to the wall there was so little clearance one had to basically shimmy past the toilet to go to or from the shower. How this ever passed inspection I'll never know - and an inspection was very likely conducted given that this bathroom was created as part of a post-fire renovation funded with insurance money (from what I've been able to gather, this occurred about five years before I acquired the property).
Here are a few shots of the bathroom:
The Issue
After purchasing a new toilet (keep reading) I discovered - I know, poor planning on my part - that the existing run of waste and soil pipe serving ths bathroom is flawed in its execution.
I should note that the exsiting branches serving the sink. the shower and the vent are all 2" Sch 40 PVC (thank goodness!) while the run from the toilet is 3" Sch 40 PVC.
Below, I've roughly hand-drawn the current drain layout (overhead view) and have also annotated some photos (compare to the drawing for context) to assist folks in hopefully seeing what I'm seeing. This looks to me like a boneheaded attempt at venting all three fixtures using a single vent (a combination dry vent and wet vent scenario) gone horribly awry.
From what I can gather, the shared vent is flawed because it goes horizontal when its still beneath the bathroom floor. As I understand it, vents can't turn horizontal until they reach 42" above the finished floor or 6" above the highest flood plane of the fixture(s) being served. I already addressed this exact problem in the ongoing kitchen renovation - the original vented kithen sink was located beneath a window and, among other problems, its vent turned horizontal well below the elevation of the rim of the sink. I fixed that (and the other problems) and the new installation now conforms to code (IPC in my state, I should note).
The Solution (at least the approach I'm thinking of taking - this is where I need advice)
I obviously want to address this latest issue.
As part of the larger renovation project that I'm accomplishing myself (jack of all trades with former pro-carpenty experience) - and to address the toilet clearance issue - I purchased an in-the-wall carrier (Gerberit for 2x4 wall) and the shallowest compatible wall hung toilet I could find (Duravit ME Compact) - this combination will provide over 22 inches of free area in front of the new toilet. Accordingly, I need to move the toilet riser from it's present location rearward into the center of the interior 2x4 wall (the wall located directly behind the existing toilet); in essence, shifting the riser's location 12-1/2" to the rear - the distance that the original riser was from the face of the wall framing (the orignal installer got one thing right).
To accomplish this, I think I can simply cut out the relevant soil and drain fitings and essentially shift the remaining components downstream to make up the difference between the orginal use of a sanitary tee laying on its back (which didn't meet code given that the distance from the rim of the closet flange to the center of the horizontal run of 3" pipe exeeded 12" - it was actually over 14 inches) and reliance instead on a combination tee (keep reading).
As an aside, I also want to change out the sink (for a shallower wall-hung version) and move its location a bit closer to the door (to provide proper space between it and the toilet) and will be relocating its riser plus running the copper supply pipes from where they currently emerge up through the floor into the wall so that, in the end, nothing will be mounted to the floor - everything will be wall-hung (and this includes a short of run of hydonic baseboard heat that I intend to run along the 4' length of wall next to the door; the supply and return will come up through that wall - another interior 2x4 wall - to feed it.
So, here's my rough drawing showing the current drain layout (overhead view):
The lower right hand corner depicts the bathroom door. The upper left hand corner is the shower. The upper right hand corner is the plumbng chase that conceals the shower'shot and cold water supplies and also the vent. To the rght is the wall to the bathroom where the sink riser is located (and where I intend to locate the riser for the in-the-wall toilet tank/carrier). The carrier wll be concealed behind a piece of cabinet grade birch plywod that will cover the entire installation making for simple removal should any part of the carrier or associated plumbing need to be accessed in the future (the birch panel will be screwed to the framing using stainless steel screws and finish washers, this will offer a stable mounting surface for the wall-mounted toilet and give me some piece of mind about any future need to access the entire installation.
And here are the annotated photos accompanying the drawing (I tried to match the terms used so that folks can bettre visualize what I'm seeing):
Here's the original 3" sanitary tee w/cleanout and attached toilet riser (in correct orientation):
Looking to the right, we can see the relative locations of the shower p-trap and riser and vent (both the horizontal run and where it turns and heads up to the roof):
Assuming I can get the drainage slopes right (which I should have no problem doing given that, if need be, I can drop the entre assembly down to lower starting and ending elevations - I have that flexibilty as shown in the photo depicting the access to the crawlspace) it seems the most obvious approach is to cut off the existing p-trap serving the shower and glue in its place another p-trap that will face the location of the existing vent (where it turns vertical for the run to the roof). Then I can connect the shower's trap arm to the vent via a sanitary tee (oriented vertically) and then connect the outlet of that a horizontal run of 2" pipe that heads toward the 2" connection on the 3x3x2 wye. A 45-degree albow at the end of that run of 2' pipe will turn the corner so that it can connect to the 3x3x2 wye located just downstream of the toilet.
Oh, in the image below (which depicts my proposed solution), the highlighted components depict my reuse of exisiting components - old work - while the non-highlighted components depict new work:
As for the connection to the in-the-wall toilet, I figure I can use a 3" combination tee laid on its side (fitted with a clean-out) connecting upstream of the aforecited 3x3x2 wye to a long sweep 90-degree elbow, the latter of which will connect to the new toilet riser which, itself, will emerge dead center through the bottom plate of the 2x4 wall immediately behind wherer the oroginal riser was located (sadly, the framing of this interior wall is nominally dimensioned unlike the native framing used pretty much everywhere else - the OD of 3" Sch 40 being 3.5" and all).
As an aside, I intend to replace the existing sink/cabinet with a shallower wall-mounted unit (to further improve access to and from the toilet and shower) and will need to relocate the existing sink riser (moving it along the wall closer to the door). Thus, this approach also plays well with with the need to relocate the sink riser given that I'm already shifting the drainline assembly in the direction of the door anyways. The existing sink riser is not anywhere close to centered on the sink so I want to fix this too.
The 2" and 3" hub couplings shown in my drawing depicting my proposed approach speaks to my intent of reusing as much of the existing plumbing assembly as I can. Note - I can't account for the origins of the brown staining which covers much of the existing PVC but, assuming it scrubs off, then I'll be reusing what I can.
A quick install of some LPV flooring over the existing linoleum (I don't have time to tear into the floor right now) will, along with tiling the shower surround, finish up this bathroom sub-project.
Given the nothing will be touching the floor post-renovation I can come back at a later date and properly address the slope in the floor (it needs the joist to be shaved to make it level) followed by tileing it - a job faciliated by the future ease of pullng the wall-mounted sink and wall-mounted toilet - I'll have ready access to the entire floor in just a few minutes.
OK, is my approach sound? What did I get wrong? Is there a better solution?
I don't beleive the sink needs its own (studor) vent but that could be easily accomplished. They're approved locally and I don't mind using one in this situation.
Please know that I am grateful for whatever guidance folks can provide.
To begin, I wish to honor Terry Love (sadly deceased) and this amazing forum - what an incredible resource Mr. Love managed to assemble, a true tribute to the man who has helped so many!
Now, on to my inquiry...
So, one thing led to another and I now find myself needing to correct a drainage/venting problem.
The Situation
This matter involves a long and narrow (IOW tiny!) 3/4 bath (8' x 4') located on the ground floor above a crawlspace in one-half of a side-by-side/townhouse-style two-story duplex. As shown below, the original toilet only provided ~14" of clearance in front of the bowl - IOW from the nose of the bowl to the wall there was so little clearance one had to basically shimmy past the toilet to go to or from the shower. How this ever passed inspection I'll never know - and an inspection was very likely conducted given that this bathroom was created as part of a post-fire renovation funded with insurance money (from what I've been able to gather, this occurred about five years before I acquired the property).
Here are a few shots of the bathroom:
The Issue
After purchasing a new toilet (keep reading) I discovered - I know, poor planning on my part - that the existing run of waste and soil pipe serving ths bathroom is flawed in its execution.
I should note that the exsiting branches serving the sink. the shower and the vent are all 2" Sch 40 PVC (thank goodness!) while the run from the toilet is 3" Sch 40 PVC.
Below, I've roughly hand-drawn the current drain layout (overhead view) and have also annotated some photos (compare to the drawing for context) to assist folks in hopefully seeing what I'm seeing. This looks to me like a boneheaded attempt at venting all three fixtures using a single vent (a combination dry vent and wet vent scenario) gone horribly awry.
From what I can gather, the shared vent is flawed because it goes horizontal when its still beneath the bathroom floor. As I understand it, vents can't turn horizontal until they reach 42" above the finished floor or 6" above the highest flood plane of the fixture(s) being served. I already addressed this exact problem in the ongoing kitchen renovation - the original vented kithen sink was located beneath a window and, among other problems, its vent turned horizontal well below the elevation of the rim of the sink. I fixed that (and the other problems) and the new installation now conforms to code (IPC in my state, I should note).
The Solution (at least the approach I'm thinking of taking - this is where I need advice)
I obviously want to address this latest issue.
As part of the larger renovation project that I'm accomplishing myself (jack of all trades with former pro-carpenty experience) - and to address the toilet clearance issue - I purchased an in-the-wall carrier (Gerberit for 2x4 wall) and the shallowest compatible wall hung toilet I could find (Duravit ME Compact) - this combination will provide over 22 inches of free area in front of the new toilet. Accordingly, I need to move the toilet riser from it's present location rearward into the center of the interior 2x4 wall (the wall located directly behind the existing toilet); in essence, shifting the riser's location 12-1/2" to the rear - the distance that the original riser was from the face of the wall framing (the orignal installer got one thing right).
To accomplish this, I think I can simply cut out the relevant soil and drain fitings and essentially shift the remaining components downstream to make up the difference between the orginal use of a sanitary tee laying on its back (which didn't meet code given that the distance from the rim of the closet flange to the center of the horizontal run of 3" pipe exeeded 12" - it was actually over 14 inches) and reliance instead on a combination tee (keep reading).
As an aside, I also want to change out the sink (for a shallower wall-hung version) and move its location a bit closer to the door (to provide proper space between it and the toilet) and will be relocating its riser plus running the copper supply pipes from where they currently emerge up through the floor into the wall so that, in the end, nothing will be mounted to the floor - everything will be wall-hung (and this includes a short of run of hydonic baseboard heat that I intend to run along the 4' length of wall next to the door; the supply and return will come up through that wall - another interior 2x4 wall - to feed it.
So, here's my rough drawing showing the current drain layout (overhead view):
The lower right hand corner depicts the bathroom door. The upper left hand corner is the shower. The upper right hand corner is the plumbng chase that conceals the shower'shot and cold water supplies and also the vent. To the rght is the wall to the bathroom where the sink riser is located (and where I intend to locate the riser for the in-the-wall toilet tank/carrier). The carrier wll be concealed behind a piece of cabinet grade birch plywod that will cover the entire installation making for simple removal should any part of the carrier or associated plumbing need to be accessed in the future (the birch panel will be screwed to the framing using stainless steel screws and finish washers, this will offer a stable mounting surface for the wall-mounted toilet and give me some piece of mind about any future need to access the entire installation.
And here are the annotated photos accompanying the drawing (I tried to match the terms used so that folks can bettre visualize what I'm seeing):
Here's the original 3" sanitary tee w/cleanout and attached toilet riser (in correct orientation):
Looking to the right, we can see the relative locations of the shower p-trap and riser and vent (both the horizontal run and where it turns and heads up to the roof):
Assuming I can get the drainage slopes right (which I should have no problem doing given that, if need be, I can drop the entre assembly down to lower starting and ending elevations - I have that flexibilty as shown in the photo depicting the access to the crawlspace) it seems the most obvious approach is to cut off the existing p-trap serving the shower and glue in its place another p-trap that will face the location of the existing vent (where it turns vertical for the run to the roof). Then I can connect the shower's trap arm to the vent via a sanitary tee (oriented vertically) and then connect the outlet of that a horizontal run of 2" pipe that heads toward the 2" connection on the 3x3x2 wye. A 45-degree albow at the end of that run of 2' pipe will turn the corner so that it can connect to the 3x3x2 wye located just downstream of the toilet.
Oh, in the image below (which depicts my proposed solution), the highlighted components depict my reuse of exisiting components - old work - while the non-highlighted components depict new work:
As for the connection to the in-the-wall toilet, I figure I can use a 3" combination tee laid on its side (fitted with a clean-out) connecting upstream of the aforecited 3x3x2 wye to a long sweep 90-degree elbow, the latter of which will connect to the new toilet riser which, itself, will emerge dead center through the bottom plate of the 2x4 wall immediately behind wherer the oroginal riser was located (sadly, the framing of this interior wall is nominally dimensioned unlike the native framing used pretty much everywhere else - the OD of 3" Sch 40 being 3.5" and all).
As an aside, I intend to replace the existing sink/cabinet with a shallower wall-mounted unit (to further improve access to and from the toilet and shower) and will need to relocate the existing sink riser (moving it along the wall closer to the door). Thus, this approach also plays well with with the need to relocate the sink riser given that I'm already shifting the drainline assembly in the direction of the door anyways. The existing sink riser is not anywhere close to centered on the sink so I want to fix this too.
The 2" and 3" hub couplings shown in my drawing depicting my proposed approach speaks to my intent of reusing as much of the existing plumbing assembly as I can. Note - I can't account for the origins of the brown staining which covers much of the existing PVC but, assuming it scrubs off, then I'll be reusing what I can.
A quick install of some LPV flooring over the existing linoleum (I don't have time to tear into the floor right now) will, along with tiling the shower surround, finish up this bathroom sub-project.
Given the nothing will be touching the floor post-renovation I can come back at a later date and properly address the slope in the floor (it needs the joist to be shaved to make it level) followed by tileing it - a job faciliated by the future ease of pullng the wall-mounted sink and wall-mounted toilet - I'll have ready access to the entire floor in just a few minutes.
OK, is my approach sound? What did I get wrong? Is there a better solution?
I don't beleive the sink needs its own (studor) vent but that could be easily accomplished. They're approved locally and I don't mind using one in this situation.
Please know that I am grateful for whatever guidance folks can provide.