I am adding a bathroom to my upstairs and want to make sure my venting is correct. I will be tying my sinks, toilet, and shower together. My shower venting is a little weird and want to make sure it works. The shower is in the middle of the room and because of that I need to run about 4 feet horizontally before being able to go vertical. It seems as though you need to wet vent it to do that and a dry vent will not work. Because of that I was planning on tying my sink drainage to the shower wet vent which eventually ties in with the toilet drainage. Will this work or do I have a better option? I included a crude sketch of what I am talking about. Thanks for your help.

20210715_163016.jpg
 

Jeff H Young

In the Trades
Messages
8,991
Reaction score
2,250
Points
113
Location
92346
Wait a minute 2 inch dry vent serving water closet probebly almost surely not meeting code and likly can be eliminated but cant be left alone. technicaly
 

wwhitney

In the Trades
Messages
6,579
Reaction score
1,852
Points
113
Location
Berkeley, CA
How's that? Reach4's diagram looks like a compliant UPC wet vent to me. The WC has a 2" vent. The 2" segment from shower to the 3" WC fixture drain is carrying 4 DFUs, which is the maximum for a 2" horizontal wet vent, but is allowed.

Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,991
Reaction score
2,250
Points
113
Location
92346
How's that? Reach4's diagram looks like a compliant UPC wet vent to me. The WC has a 2" vent. The 2" segment from shower to the 3" WC fixture drain is carrying 4 DFUs, which is the maximum for a 2" horizontal wet vent, but is allowed.

Cheers, Wayne
I was refering to go hawks sketch. reach 4 nailed it! i didnt notice he had eliminated the illegal flat vent on W/C thanks wayne no one mentioned the other vent just details on the wet vent
 