The code sections (UPC 417.3 or IPC 424.2) don't call out a vacuum breaker in particular, just an ASME A112.18.3 backflow prevention device. Not my area of expertise, but it appears there are dual check valve devices that meet ASME A112.18.3. So maybe you can install a dual check valve or similar backflow preventer that won't discharge water?
Cheers, Wayne
I'll have to do more research in what types of double checks I can install that are reasonable to install. I really don't want to install this style of double check
which requires maintenance and I believe that these require specific location restrictions for testing.. ie, can not be installed too low or too high.
ignoring the words written in the instruction and looking at the diagram only. I see this device installed on the mixed water inlet to your roman tub spout and when pulling the lift knob on the spout it diverts to the handspray. Installing a water hammer arrestor in this type of install is weird but does make more sense then a vacuum breaker...
thats my two cents.
good luck.
Its kinda weird. The water hammer arrestor is specifically called a VacuRester.. or some such. Kohler tech couldn't tell me what its function is. Maybe if I present the gobbledeygook manual to the inspector I can bamboozle them into signing off.
no way they make em in that finish. chrome or rough brass, all ugly.
there is a check valve already on that Kohler faucet.
WHammer arrestor is nonsense.
I had a project in the 90s with this exact scenario. Inspector insisted that the backflow of the diverter was not and approved device. So I threaded a 6" brass nipple and rough brass vacuum breaker onto the hose and inserted it into the deck mounted holder for inspection with the hose and handheld dangling in the tub. The inspector signed me off but asked "if I was going to remove the vacuum breaker?".. "Yes.. as soon as the door closes behind you". I will go this route again if needed.
Im not familiar with this particular valve . but reading the kohler instructions they recomend using the 652 ad which is a water hammer arrestor so why not install that ? I doubt this valve dosent conform to upc after taking second look I dont see a reason you cant install the water hammer aresstor its clear thats what they want its nothing to do with cross contamination
I've never installed this one either. I should have it in stock soon, so I'll get to futz with it for a bit before I send it out. I just would rather have something in place before we place a slab of quartz stone over the top of the tub and the entire works become inaccessible.