I have a Grundfos pump about 35 feet down my well. It delivers just under 11 GPM (measured) at the shut off pressure of 70PSI. The 1" poly line runs about 50 feet outside the house and about 70 feet inside. I'm doing some re-plumbing and it would not be too difficult to add a water hammer arrestor just inside the house on that 1" line. The only check valve is in the pump. Think it would be worthwhile?
 

Mowmow

New Member
Messages
18
Reaction score
0
Points
1
Location
Ohio
I would think that the closer to the pump the better. What am I missing? Or is the hammer associated with 70PSI (plus a bit of water column) and 120 feet of 1" poly against the pump's check valve negligible?
 
Last edited:

Valveman

Cary Austin
Staff member
Messages
14,667
Reaction score
1,314
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
If you are getting water hammer it is from the check valve slamming when the pump stops abruptly from 11 GPM, as the check is wide open. When using a Cycle Stop Valve the tank is being filled at 1 GPM, and the check valve is barely open and there is no water hammer when the pump shuts off. It is best to prevent water hammer and water hammer is hard to catch, even with an arrestor once it is in motion.
 

Mowmow

New Member
Messages
18
Reaction score
0
Points
1
Location
Ohio
Thanks Valveman. Totally makes sense - that is what I was trying to describe. I just don't know how durable the pump's check valve is. I would think they are designed to handle their design total head and GPM combo, and wondered if adding an arrestor mid-stream might cut the effective hammer in half. I'm not noticing much at the tank end, but it's the pump end that I was interested in - whether it is noisy or not, less stress is less stress.
 

Mowmow

New Member
Messages
18
Reaction score
0
Points
1
Location
Ohio
No. Why do you ask? Do you have a symptom?
No visible symptoms. Just a matter of: can I do something that might help at minimal cost. I recall seeing threads on this site that talk about check valve life. I'm aware of the cycle stop technology and am not ready to switch over to that.
Water velocity is a big factor in water hammer. Larger pipe would help.
Interesting point. Thanks.
 

Reach4

Well-Known Member
Messages
38,964
Reaction score
4,463
Points
113
Location
IL
Symptom would be audible for water hammer. You already have what constitutes a very very large water hammer arrestor, as LLigetfa pointed out. So a separate water hammer arrestor would do nothing, other than possibly giving somebody a chuckle. Like people doing a flash photo of the moon.

But while replumbing, show us a photo of the pipe from your well, the input to your pressure tank, your pressure gauge, drain valve, pressure switch, and chances are we will point out a suggested improvement.
 

Mowmow

New Member
Messages
18
Reaction score
0
Points
1
Location
Ohio
Just trying to do what I can for minimal cost.

Thanks everyone!
 