I'm helping a friend with his well setup and I wanted to get some advise. There's a submersible pump in the well which then leads to a check valve, then a T fitting for the pressure switch and another T for the pressure tank - unfortunately I don't have any details on the pump model or its depth. From there the pipe travels up to a 5000 gallon storage tank and there's a float valve to shut off the water which in-turn causes the pressure to rise and trigger the pressure switch by the pump. There is another pump that then pumps the water to the house, so the submersible pump is only pumping water from the well to the storage tank and not providing water directly to the home. Unfortunately I don't know how many feet of water head I have between the tank and the pressure switch because someone installed the pressure gauge on the pump side of the check valve instead of next to the pressure switch, so I will be fixing that tomorrow so then I can have an accurate measurement. It seems to be about 30ft of elevation gain and about a 100ft run of 1" pipe. When the pump is running, the pressure reading is 15 PSI and I'd venture to guess it's somewhere around 5-10 GPM of flow based on looking at it - I have yet to verify that.
We just changed out an old Square D pressure switch (which is labeled as a 20/40) because it stopped working (contacts were shot), but based on how the recently installed pressure tank was configured (38 PSI), I was skeptical that the switch was actually set for 20/40 because that's how the tank should be configured for 40/60 pressure switch (I'm guessing they just left the tank at the factory-set pressure). So I made up a fixture and tested the switch and it is configured for 33/55, so I'm guessing that someone bumped up the range, and the 2 PSI difference is probably within the error of an old switch (i.e. I doubt they changed the differential significantly). Either way, the recent service to have the tank installed wasn't done correctly.
When I first installed the new switch (configured for 20/40), it would get into an on/off oscillation when the float was raised/lowered too fast, so I'm guessing we're running into a water hammer issue, so for the time-being I raised the pressure cutoffs to 30/50 which alleviated that (with the incorrectly configured pressure tank), but it's only until the float valve really closes that the pressure starts to slowly climb until it reaches 50 PSI. If you leave the float valve closed, the pump can reach 70 PSI after a while, but it seems like it's working hard above 40 PSI to reach that point.
So, it seems like there are a few issues - there's a potential water hammer issue, the pressure switch is set higher than it needs to be, and the pressure tank is not configured correctly. Here's what I was thinking - what if I set the pressure switch down to 20/40, drop the pressure tank to 18 PSI, and then put a check valve just after (downstream) of the pressure switch to stop the oscillations from reaching the pressure switch - does this sound like a feasible solution? Or, if I were to drop the pressure tank down to it's correct cutin pressure-2 PSI value, would that alone alleviate the oscillations affecting the pressure switch and avoid the need for another check valve after the pressure switch?
One other thing - should float valves require a lot of upward force to stop the water flow at 50 PSI (or even 30 PSI), and/or does that required amount of upward force decrease when the system is at a lower PSI? I noticed that it took a good amount of upwards force for the float to finally shut off the water. In other words, does the upward force required to close a check valve increase with the PSI in the pipe it's closing off, or does it sound like the valve probably needs to be replaced? What was happening is that pressure would build, shut off the pump, but water was still coming out of the float valve (slowly) and eventually the pump would kick back on, build up pressure, and it would eventually shut off again.... just seemed a little strange. A properly adjusted pressure tank here would probably help with runtimes regardless, but I was curious as to whether those float valves are meant to shut off at a set deflection, regardless of system PSI.
Thanks!!
We just changed out an old Square D pressure switch (which is labeled as a 20/40) because it stopped working (contacts were shot), but based on how the recently installed pressure tank was configured (38 PSI), I was skeptical that the switch was actually set for 20/40 because that's how the tank should be configured for 40/60 pressure switch (I'm guessing they just left the tank at the factory-set pressure). So I made up a fixture and tested the switch and it is configured for 33/55, so I'm guessing that someone bumped up the range, and the 2 PSI difference is probably within the error of an old switch (i.e. I doubt they changed the differential significantly). Either way, the recent service to have the tank installed wasn't done correctly.
When I first installed the new switch (configured for 20/40), it would get into an on/off oscillation when the float was raised/lowered too fast, so I'm guessing we're running into a water hammer issue, so for the time-being I raised the pressure cutoffs to 30/50 which alleviated that (with the incorrectly configured pressure tank), but it's only until the float valve really closes that the pressure starts to slowly climb until it reaches 50 PSI. If you leave the float valve closed, the pump can reach 70 PSI after a while, but it seems like it's working hard above 40 PSI to reach that point.
So, it seems like there are a few issues - there's a potential water hammer issue, the pressure switch is set higher than it needs to be, and the pressure tank is not configured correctly. Here's what I was thinking - what if I set the pressure switch down to 20/40, drop the pressure tank to 18 PSI, and then put a check valve just after (downstream) of the pressure switch to stop the oscillations from reaching the pressure switch - does this sound like a feasible solution? Or, if I were to drop the pressure tank down to it's correct cutin pressure-2 PSI value, would that alone alleviate the oscillations affecting the pressure switch and avoid the need for another check valve after the pressure switch?
One other thing - should float valves require a lot of upward force to stop the water flow at 50 PSI (or even 30 PSI), and/or does that required amount of upward force decrease when the system is at a lower PSI? I noticed that it took a good amount of upwards force for the float to finally shut off the water. In other words, does the upward force required to close a check valve increase with the PSI in the pipe it's closing off, or does it sound like the valve probably needs to be replaced? What was happening is that pressure would build, shut off the pump, but water was still coming out of the float valve (slowly) and eventually the pump would kick back on, build up pressure, and it would eventually shut off again.... just seemed a little strange. A properly adjusted pressure tank here would probably help with runtimes regardless, but I was curious as to whether those float valves are meant to shut off at a set deflection, regardless of system PSI.
Thanks!!