I have read numerous posts on these forums about the subject but questions remain for my situation.
I am connected to the city water utility with a 3/4" meter, there is a 3/4" PVC pipe entering the house from the meter and a 1" copper manifold that provides home-run service to each fixture via PEX-B of various sizes.
Question 1: is 1/2" PEX large enough to supply hot and cold water to my shower mixing valve from the manifold?
I am connected to the city water utility with a 3/4" meter, there is a 3/4" PVC pipe entering the house from the meter and a 1" copper manifold that provides home-run service to each fixture via PEX-B of various sizes.
Question 1: is 1/2" PEX large enough to supply hot and cold water to my shower mixing valve from the manifold?
- The shower valve can simultaneously supply two shower heads (a rain shower and hand shower). The rain shower head has a 2.5 GPM (gallons per minute) flow and the hand-shower is 1.5 GPM.
- Depending on the temperature mix (balance of hot/cold, per the user's desired temperature), let's say it's 75% hot and 25% cold; that would demand 3 GPM from the hot supply and 1 GPM from the cold supply. Or, maybe the user is a lunatic and wants 100% hot or a complete psycho and wants 100% cold, then hot or cold would need to provide the full 4 GPM. For 1/2" PEX, this would require a sustained water velocity of 7.24 FPS (feet per second). Is this possible? Within reason for PEX to transport water at this velocity? Within reason for the water from the city to provide ample pressure (PSI, pounds/square inch) to force water through tubes at this velocity?
- There are different flavors of rough mixing valve available, I can get a valve with 1/2" PEX crimp ports or a valve with 1/2" - 14 NPT OD 5/8" ID For 1/2" Nom. Copper Tubing. I can use the copper port version to connect 3/4" PEX adapters and run 3/4" PEX hot and cold lines directly from the manifold to the shower valve.
- This tub/shower valve has all [1/2" - 14 NPT OD 5/8" ID For 1/2" Nom. Copper Tubing] ports. So the pipe running from the valve to the tub faucet is 1/2" copper.
- Again, user-preference of the bather becomes a factor. If the bather is nuts (or an elite athlete) and wants to take an ice bath, then the cold supply line will be solely responsible for providing the GPM to fill the tub. Likewise for someone who wants to take a near scalding-hot bath, the hot side is providing everything.
- My plan is to run 3/4" PEX from the manifold directly to this tub/shower valve, with 3/4" PEX to 1/2" Copper adapters directly preceding entry to the valve. Tub fill performance is still limited by the 1/2" copper tub faucet line (so, yes 3/4" PEX is overkill perhaps, but necessary to overcome the limits of 1/2" PEX's inner diameter of 0.475 inches for tub filling purposes). Is this a rational plan? Would 1/2" PEX be sufficient and I just wait a little bit longer for the tub to fill up? What is a reasonable expectation for water velocity in FPM through 1/2" PEX with average residential PSI from city utility?