B VENT Install For Water Heater

Users who are viewing this thread

Mitch Sutherland

In the Trades
Messages
5
Reaction score
0
Points
1
Location
Indiana
I am installing a 3 inch B vent for a water heater. I am 31 inches from the ridge vent. I have a 5-12 roof pitch. I read the code stating must be 2 feet taller than any 10 foot horizontal structure. Does this include the roof? To be 2 feet taller than the ridge vent/peak I would be nearly 3.5 foot in the air with the B vent. Is there another code I am missing thank you! Any help would be appreciated!
 

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,460
Points
113
Not sure what code you are under but... UPC table 509.6.2 incidates with 6/12 or under with listed pipe and listed cap. Should extend minimum 12" from the highest portion of the roof where its penetrating to the lowest portion of the discharge opening.
 