Are recirculating loops/pumps dangerous for my house?

Users who are viewing this thread

JoeSD

New Member
Messages
15
Reaction score
1
Points
3
Location
San Diego
When we remodeled our house in 2016 we had the whole house replumbed and they put in a recirc loop with dedicated return line. I've recently read though that recirc loops are notorious for causing copper issues due to the high velocity and hot water. Should I just turn the pump off and stop using recirc line?
 

Breplum

Licensed plumbing contractor
Messages
2,186
Reaction score
915
Points
113
Location
San Francisco Bay Area
Well, we certainly don't like to see short turn copper 90s and such. The primary issue is high velocity pumps installed by idiots who don't know what they are doing.
Make sure you have low velocity and you should be good.
 

John Gayewski

In the Trades
Messages
4,647
Reaction score
1,495
Points
113
Location
Iowa
What size pipe did they use. 1/2 pipe was the norm for a long time which did cause velocity issues. As long as the recirc line is 3/4" pipe you should be good. That is, as long as you have the smallest pump made for these things.
 
Last edited:

Fitter30

Well-Known Member
Messages
4,778
Reaction score
922
Points
113
Location
Peace valley missouri
Ask yourself can i hear loud water noises rushing through the pipes? Not don't worry about it. Never have seen copper pipe erosion in 40 years.
 

Tuttles Revenge

In the Trades
Messages
4,458
Reaction score
1,569
Points
113
I have seen copper pipe wear out from too much velocity in a too small recirc line. Happened on a job the second day after start of work and the homeowner thought the carpenters caused it. We ended up replacing the 1/2" copper return with a 3/4 PEX with lower volume pump.
 

JoeSD

New Member
Messages
15
Reaction score
1
Points
3
Location
San Diego
Ask yourself can i hear loud water noises rushing through the pipes? Not don't worry about it. Never have seen copper pipe erosion in 40 years.
I can't hear any water rushing its always dead silent.
What size pipe did they use. 1/2 pipe was the norm for a long time which did cause velocity issues. As long as the recirc line is 3/4" pipe you should be good. That is, as long as you have the smallest pump made for these things.
I went and looked, he used 1/2" pipe, it was done back in 2016. Disappointing he didn't use 3/4"

Well, we certainly don't like to see short turn copper 90s and such. The primary issue is high velocity pumps installed by idiots who don't know what they are doing.
Make sure you have low velocity and you should be good.
I was here a lot when they were renovating the house and replumbing everything and saw everything with the walls opened, the recirc loop is a big long run from the garage to the kitchen with lots of straight and not many turns. I found the model of the pump, it's a GrundFos UP 15-10 B5/TLC with a flow rate of 2.77 US GPM. Is that low or high velocity?
 

Fitter30

Well-Known Member
Messages
4,778
Reaction score
922
Points
113
Location
Peace valley missouri
I can't hear any water rushing its always dead silent.

I went and looked, he used 1/2" pipe, it was done back in 2016. Disappointing he didn't use 3/4"


I was here a lot when they were renovating the house and replumbing everything and saw everything with the walls opened, the recirc loop is a big long run from the garage to the kitchen with lots of straight and not many turns. I found the model of the pump, it's a GrundFos UP 15-10 B5/TLC with a flow rate of 2.77 US GPM. Is that low or high velocity?
max flow 3.2 gpm
100' 1/2". m holds 1.2 gallons
100' 3/4" m holds 2.25 gallons
 

John Gayewski

In the Trades
Messages
4,647
Reaction score
1,495
Points
113
Location
Iowa
Roughly a 1/2" line at 2.8gpm should be traveling at around 3ft.per sec

At 3.2 gpm it should be about 3.4 ft per sec.

You should be under the max for 1/2copper. Which (going from memory) is about 4ft per sec.

If that pump does what you say it does you should be good.
 

John Gayewski

In the Trades
Messages
4,647
Reaction score
1,495
Points
113
Location
Iowa
Screenshot_20240507-090225_Chrome.jpg
 

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,472
Points
113
Location
92346
I dont know the tricks to dialing in the system but a flow control "circuite setter" can slow it down a bit more if you want ? getting effeciency I dont know there again are a lot of factors , a whole house recirculating system thats left on and allowed to run and keep pipes hot a bit differant from one where you walk in a bathroom and the system kicks on and gets hot water to the area that might take more speed to do it quickly but pump runs shorter amounts of time.
But a well plumbed recirc system should be enjoyed and last a long time I wouldnt expect cost a bunch in energy if done right
 