I'm reviewing plans for new restaurant and on the Mechanical plans the Make-Up Air unit is rated at 230 volts and the equipment schedule on the Electrical plans is calling for 208 volts.

There is no mention of a transformer or booster. Is this going to be a problem that needs to be addressed by the engineer?

What happens if there's a voltage drop of 1%?

208v -1% drop = 205.92 volts

What happens if there's a voltage drop of 3%?

208v - 3% = 201.76 volts

or even 5% = 197.6?
 

frenchelectrican

Electrician
Messages
46
Reaction score
0
Points
0
Location
NE Wis / Paris France { In France now }
Yes and No depending on the nameplate on that equment if the nameplate say 230-208 volts and also pretty good percentage of them will list the min and max operating voltage range.

also i dont know why if the Mech plans spec'ed on 230 volts and the Elec plans spec'ed on 208 i am thinking somewhere along the line there is a " commuation " or "information " mixed up or not getting right information.

if this is on new condustucion it should be seen that right away when whoever is responable with the prints

I will let some of the HVAC and Electrician crews chime in here as well i think they will tell you very simuair what i am saying with this and they can add few more info along the way.

Merci, Marc
 

hj

Master Plumber
Messages
33,611
Reaction score
1,051
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
power

Is there 3-phase power here?
I've never seen a 208/120 system that was not 3 phase. Most units will operate with a 10% voltage disparity, but a dedicated 208 unit would be better.
 

Jimbo

Plumber
Messages
8,918
Reaction score
19
Points
0
Location
San Diego, CA
You need to have equipment which is also rated at 230/208. It's the motors that matter. Many motors are in fact listed at 230/208. If it is listed as just 230, I don't think you can run it on 208, but check with the company. Equipment which is dual rated, will either have just one hookup, and the specs will be dual rated, with lower BTU,CFM, whatever, at 208. Or, it will have different taps for the two voltages, and currents will be higher at 208.
 

frenchelectrican

Electrician
Messages
46
Reaction score
0
Points
0
Location
NE Wis / Paris France { In France now }
hj said:
Is there 3-phase power here?
I've never seen a 208/120 system that was not 3 phase. Most units will operate with a 10% voltage disparity, but a dedicated 208 unit would be better.


Sure you will see the 208/120 volt in single phase as well that will be feed off from the 3Ø network this is common to find in large area like condo , megsized resdentail area, commercal area

but just wait until the OP comeback in here and comfermed the question but i am pretty much sure it is 3Ø system there

Merci , Marc
 