Rossn
Member
Have a few pressure challenges, and looking for some insight.
TLDR: have some long distances to run cold water in my house, and would like to understand:
Questions:
- For an above-garage apartment (1 bedroom, small kitchen, 3/4 bath, washer dryer), is it appropriate oversize the plumbing from the planned 3/4" PEX trunk (31 psi) to 1" Pex (33 psi) or 3/4" copper (34 psi)?
- For a hose bibb off the garage, is it appropriate to oversize the plumbing from the planned 3/4" PEX line (36 psi) to 1" pex line (39.5 psi)?
- Are there shower heads that perform acceptably in the 30-35 psi range? My understanding is that most require 40 psi.
- If I cannot get sufficient pressure at my furthest fixture, what are my options?
Background:
My house is on city water, and sees about 51 PSI at the entry point to the house, which has a calculated demand of 40 WSFUs/26 GPM (4-1/2 baths, 1-1/2 kitchens). As part of a deep remodel, the (new) main trunk (1-1/4", then 1" Copper) runs about 155 (equivalent) feet to the garage. From the garage to the furthest fixture (shower) in a garage apartment is another 65 (equivalent) feet. Additionally, there is a hose bib that will run from the garage another 50 (equivalent) feet, and will need to see 7.5 GPM.
Calculations, per IRC, give the pressures I've listed.
Main distribution line:
1" Meter is at the street and supply line runs about 280' to the house. Currently 1" copper, it is insufficient to meet the needs of the 40 WSFUs/26 GPM calculated demand of the house (does not consider irrigation needs). That will need to be upgraded to 1-1/2", but will be more complicated/expensive due to a county irrigation ditch it must traverse. So, that will be handled after the remodel is completed. Certainly the apartment shower isn't going to work well before that happens.
Thank you!
TLDR: have some long distances to run cold water in my house, and would like to understand:
Questions:
- For an above-garage apartment (1 bedroom, small kitchen, 3/4 bath, washer dryer), is it appropriate oversize the plumbing from the planned 3/4" PEX trunk (31 psi) to 1" Pex (33 psi) or 3/4" copper (34 psi)?
- For a hose bibb off the garage, is it appropriate to oversize the plumbing from the planned 3/4" PEX line (36 psi) to 1" pex line (39.5 psi)?
- Are there shower heads that perform acceptably in the 30-35 psi range? My understanding is that most require 40 psi.
- If I cannot get sufficient pressure at my furthest fixture, what are my options?
Background:
My house is on city water, and sees about 51 PSI at the entry point to the house, which has a calculated demand of 40 WSFUs/26 GPM (4-1/2 baths, 1-1/2 kitchens). As part of a deep remodel, the (new) main trunk (1-1/4", then 1" Copper) runs about 155 (equivalent) feet to the garage. From the garage to the furthest fixture (shower) in a garage apartment is another 65 (equivalent) feet. Additionally, there is a hose bib that will run from the garage another 50 (equivalent) feet, and will need to see 7.5 GPM.
Calculations, per IRC, give the pressures I've listed.
Main distribution line:
1" Meter is at the street and supply line runs about 280' to the house. Currently 1" copper, it is insufficient to meet the needs of the 40 WSFUs/26 GPM calculated demand of the house (does not consider irrigation needs). That will need to be upgraded to 1-1/2", but will be more complicated/expensive due to a county irrigation ditch it must traverse. So, that will be handled after the remodel is completed. Certainly the apartment shower isn't going to work well before that happens.
Thank you!