In my home, I sized (Per IRC) the cold water trunk on the west side of the house at 1-1/4" copper and east side side of the house at 1" copper. I am now extending the 1" from the east side of the house to the garage and hoping to confirm sizing of that last section of the trunk as 3/4" or 1" type L copper.
The garage (and apartment, above) will include:
(1) 3/4 bathroom
1 kitchen
1 clothes washer
1 exterior hose bib (3/4" pex)
1 laundry tray
Any reason to not run the trunk extension (to the garage) as 1"? I'd mainly be concerned about velocities that are low at times, and any health concerns that could come from low water velocities.
Additional information
I get 8.2 WSFUs, which translates to 12.8 GPM, but that is likely only to be seen if the space above the garage is actually rented, and when it is not, usage will be rather low.
From the former trunk, the extension it will run about 25' on a convoluted run to a pex manifold with (3) 90's & (4) 45's along the way. Pex runs from the manifold will be 20-35' to final destinations.
Pressure here is about 50 psi where it enters the home... about 110' by the pipe to the pex manifolds in the garage.
Copper.org handbook seems to indicate 3/4" pressure drop per foot starts to cap out at 10 GPM.
In my home, I sized (Per IRC) the cold water trunk on the west side of the house at 1-1/4" copper and east side side of the house at 1" copper. I am now extending the 1" from the east side of the house to the garage and hoping to confirm sizing of that last section of the trunk as 3/4" or 1" type L copper.
The garage (and apartment, above) will include:
(1) 3/4 bathroom
1 kitchen
1 clothes washer
1 exterior hose bib (3/4" pex)
1 laundry tray
Any reason to not run the trunk extension (to the garage) as 1"? I'd mainly be concerned about velocities that are low at times, and any health concerns that could come from low water velocities.
Additional information
I get 8.2 WSFUs, which translates to 12.8 GPM, but that is likely only to be seen if the space above the garage is actually rented, and when it is not, usage will be rather low.
From the former trunk, the extension it will run about 25' on a convoluted run to a pex manifold with (3) 90's & (4) 45's along the way. Pex runs from the manifold will be 20-35' to final destinations.
Pressure here is about 50 psi where it enters the home... about 110' by the pipe to the pex manifolds in the garage.
Copper.org handbook seems to indicate 3/4" pressure drop per foot starts to cap out at 10 GPM.