I'm adding a well pump circuit to an existing electric system.
There is an electric meter and main breaker panel in Barn A. There is an 100A breaker in the panel and 3 wires , (2 hots, one neutral?) are buried underground to feed a panel in Barn B. I ran a NM cable from that panel (defined as a subpanel?) to a well pump switch inside Barn B.
Is the existing subpanel properly grounded? All the neutral and ground conductors are screwed to the single busbar which is bonded to the enclosure
some related discussion with the gist that subpanels should have their own ground electrodes and not be bonded to neutral, at least for new work
There is an electric meter and main breaker panel in Barn A. There is an 100A breaker in the panel and 3 wires , (2 hots, one neutral?) are buried underground to feed a panel in Barn B. I ran a NM cable from that panel (defined as a subpanel?) to a well pump switch inside Barn B.
Is the existing subpanel properly grounded? All the neutral and ground conductors are screwed to the single busbar which is bonded to the enclosure
some related discussion with the gist that subpanels should have their own ground electrodes and not be bonded to neutral, at least for new work
why is a service neutral grounded but not the subpanel-neutral?
I know it's code (refer to NEC 250.24(A)5 and 250.32), but I don't understand why you can't use a bonding jumper to connect the ground bus and neutral bus in the subpanel? I've been told it's because