I have a 20 year old Super Hot Saturn Series 270K BTU boiler. It provides heat for an indirect water tank and 6 radiant floor zones.
Its working fine and I've never had any trouble with it for 20 years.


Mostly out of curiosity, I have "instrumented" my heating system. I can see/record when zone valves open/close, when the boiler fires and also temperatures at several points of interest.
Turns out this boiler is just down the hallway from my home office. Sometimes I can hear the boiler fire from my office. One of the things I've noticed (and a reason why I installed the instrumentation) is the boiler seems to run for short periods.
A zone will open demanding heat. This will cool the primary loop and eventually the boiler will fire. Typically the boiler will fire for just a minute or two bringing the primary loop back to its high set point.
Here's the weird part. Not infrequently, the boiler will fire about 2 seconds?? And then there is a short delay, and will then fire for longer, maybe 2 minutes.
I don't really know how the boiler controller works, but here is my theory for this behavior. Boiler senses heat demand in the primary loop. It first lights the pilot, waits for a hot pilot indication and then fires the main burner. For some reason, (electrical noise caused by the main boiler?) it decides the pilot is not hot enough, turns off the main burner and waits for the pilot temperature sensor to indicate sufficient pilot temperature and then finally runs the main burner long enough to trip the high set point.
Since it ain't broke, I don't intend to fix it, but perhaps somebody with more in depth boiler knowledge can clue me in on this behavior.
Below is a record of firing the boiler main burner. When the last number is 1, the main boiler is firing. The main boiler fires for 2 seconds, then shuts off for about 7 seconds. On again for 72 seconds. Off for 9 seconds and on again for 86 seconds. I would think that hysteresis of the low/high set points and thermal mass of the primary loop would disallow this sort of behavior??
boiler 2023-03-22 11:17:33.907509 1
boiler 2023-03-22 11:17:35.913209 0
boiler 2023-03-22 11:17:42.932223 1
boiler 2023-03-22 11:18:54.196067 0
boiler 2023-03-22 11:19:03.216447 1
boiler 2023-03-22 11:20:29.526114 0
Its working fine and I've never had any trouble with it for 20 years.
Mostly out of curiosity, I have "instrumented" my heating system. I can see/record when zone valves open/close, when the boiler fires and also temperatures at several points of interest.
Turns out this boiler is just down the hallway from my home office. Sometimes I can hear the boiler fire from my office. One of the things I've noticed (and a reason why I installed the instrumentation) is the boiler seems to run for short periods.
A zone will open demanding heat. This will cool the primary loop and eventually the boiler will fire. Typically the boiler will fire for just a minute or two bringing the primary loop back to its high set point.
Here's the weird part. Not infrequently, the boiler will fire about 2 seconds?? And then there is a short delay, and will then fire for longer, maybe 2 minutes.
I don't really know how the boiler controller works, but here is my theory for this behavior. Boiler senses heat demand in the primary loop. It first lights the pilot, waits for a hot pilot indication and then fires the main burner. For some reason, (electrical noise caused by the main boiler?) it decides the pilot is not hot enough, turns off the main burner and waits for the pilot temperature sensor to indicate sufficient pilot temperature and then finally runs the main burner long enough to trip the high set point.
Since it ain't broke, I don't intend to fix it, but perhaps somebody with more in depth boiler knowledge can clue me in on this behavior.
Below is a record of firing the boiler main burner. When the last number is 1, the main boiler is firing. The main boiler fires for 2 seconds, then shuts off for about 7 seconds. On again for 72 seconds. Off for 9 seconds and on again for 86 seconds. I would think that hysteresis of the low/high set points and thermal mass of the primary loop would disallow this sort of behavior??
boiler 2023-03-22 11:17:33.907509 1
boiler 2023-03-22 11:17:35.913209 0
boiler 2023-03-22 11:17:42.932223 1
boiler 2023-03-22 11:18:54.196067 0
boiler 2023-03-22 11:19:03.216447 1
boiler 2023-03-22 11:20:29.526114 0