Navien Tankless Water Heater Comments and questions

Users who are viewing this thread

BetaNavien

New Member
Messages
4
Reaction score
0
Points
1
Location
Los Angeles
We have a Navian npe-240a2. It was installed outdoors, under a long eave of about 4 ft, a few inches below it. I can see it says that using an exterior vent, 36" of space above is required. What are the concerns of an installation like this? There is not much room on this wall, and below it is a condenser, which is why it was installed high up. Should it be vented through the roof? Thank you!
 

Fitter30

Well-Known Member
Messages
5,521
Reaction score
1,114
Points
113
Location
Peace valley missouri
With such a deep eave I'd be concerned with flue gas getting trapped underneat and migranting back through a open window especially if theres a breeze and that side of the house. Put it through the roof. Operating temps 32°f to 120° your condenser is below the heater might get above 120° if ambient temp gets to 100°.
 

Tuttles Revenge

In the Trades
Messages
4,459
Reaction score
1,575
Points
113
With such a deep eave I'd be concerned with flue gas getting trapped underneat and migranting back through a open window especially if theres a breeze and that side of the house. Put it through the roof. Operating temps 32°f to 120° your condenser is below the heater might get above 120° if ambient temp gets to 100°.
Or being sucked back into the intake. x2 for taking it up through the roof or at least to the underside of the eave vertically, then horizontally out to the edge
 