Hello,
Systems:
1. I have two identical systems (Amana-ASXC160601-BA, matched to Alpine A Coil CB60D442107000, and Air Handler/Furnace Amana-AMVC 80905CX). Installed in June 2010.
2. Ducting is in unconditioned attic.
3. Perform maintenance yearly, have systems checked professionally every two years.
Been hotter than usual out in Vegas (and other places I hear). Last Sunday, one of the units just stopped working in late afternoon, i.e. cool air turned to warm. My troubleshooting was call for cool still showed on Ecobee app and Ecobee 3 thermostat, air was still blowing high and app/thermostat showed stage 2. Outside, the fan and condenser was NOT running. Breaker in main panel not tripped, Opened up condenser panel, see 24 volts (and board has LEDs illuminated). Local 240 shutoff fuses good (multimeter check). Turned system to OFF from ecobee app. Checked Capacitor (took it out), it was within spec of capacitor rating. Air-filters were changed 2 weeks ago (changed every 60 days). Ducts were cleaned ~3 years ago. Outside condenser foam/water cleaned in spring 2023. ~ 2 hours had passed by now. I checked to condensate line (also cleaned annually) to see if any water was present, perhaps a tell that the A coil froze - Dry, not evidence of water at condensate line. I decided to turn unit back ON for Cool and unit turned on and started cooling fine. I can only surmise that this unit (my Down Stairs unit) was working so hard that a pressure or thermal switch triggered and shut the condenser unit down.... a good thing....).
Fast forward to today. Everything has been working fine or as expected. However, after lots of reading and Google searches, I decided to look at Delta T data and began measuring supply register teams.
I have results of ~24 hours of measurements in a Google Sheet here:
My high level conclusions from this data set:
1. Consider doing something more to insulate the ducting in the attic or the attic in general. House is 24 years old.. Will be focusing on Master Bedroom ducts first. Read this article located @ Green Building Advisor about an accepted practice to bury ducting in insulation, especially in dry climates like where I live (Article here: https://www.greenbuildingadvisor.com/article/ducts-in-an-unconditioned-attic#)
2. Have the Down Stair system looked at due to borderline supply (Delta T) temps as compared to the Up stair system - perhaps a low charge (but these are sealed systems, so I am skeptical that this would be a solution unless it was never charged correctly)?
Other thoughts or comments?
Systems:
1. I have two identical systems (Amana-ASXC160601-BA, matched to Alpine A Coil CB60D442107000, and Air Handler/Furnace Amana-AMVC 80905CX). Installed in June 2010.
2. Ducting is in unconditioned attic.
3. Perform maintenance yearly, have systems checked professionally every two years.
Been hotter than usual out in Vegas (and other places I hear). Last Sunday, one of the units just stopped working in late afternoon, i.e. cool air turned to warm. My troubleshooting was call for cool still showed on Ecobee app and Ecobee 3 thermostat, air was still blowing high and app/thermostat showed stage 2. Outside, the fan and condenser was NOT running. Breaker in main panel not tripped, Opened up condenser panel, see 24 volts (and board has LEDs illuminated). Local 240 shutoff fuses good (multimeter check). Turned system to OFF from ecobee app. Checked Capacitor (took it out), it was within spec of capacitor rating. Air-filters were changed 2 weeks ago (changed every 60 days). Ducts were cleaned ~3 years ago. Outside condenser foam/water cleaned in spring 2023. ~ 2 hours had passed by now. I checked to condensate line (also cleaned annually) to see if any water was present, perhaps a tell that the A coil froze - Dry, not evidence of water at condensate line. I decided to turn unit back ON for Cool and unit turned on and started cooling fine. I can only surmise that this unit (my Down Stairs unit) was working so hard that a pressure or thermal switch triggered and shut the condenser unit down.... a good thing....).
Fast forward to today. Everything has been working fine or as expected. However, after lots of reading and Google searches, I decided to look at Delta T data and began measuring supply register teams.
I have results of ~24 hours of measurements in a Google Sheet here:
Delta T 335RPC
Up System UP System ,- Reading on Stage 2 + Hi Blower Mode after 10 mins TEMP Readings Date,Time,Toy Room,Lauren Room,Small Bathroom,Office - 2nd BR,M Bedroom,M Bath - Erin,M Bath - Mark,Hallway,Supply - Main,Supply - MBR,Delta/T,Temp Thermal Efficiency LOSS from Morning Reading,Attic Temp,Outsi...
docs.google.com
My high level conclusions from this data set:
1. Consider doing something more to insulate the ducting in the attic or the attic in general. House is 24 years old.. Will be focusing on Master Bedroom ducts first. Read this article located @ Green Building Advisor about an accepted practice to bury ducting in insulation, especially in dry climates like where I live (Article here: https://www.greenbuildingadvisor.com/article/ducts-in-an-unconditioned-attic#)
2. Have the Down Stair system looked at due to borderline supply (Delta T) temps as compared to the Up stair system - perhaps a low charge (but these are sealed systems, so I am skeptical that this would be a solution unless it was never charged correctly)?
Other thoughts or comments?