Seems a bit overkill. The
AOU36RLXFZH is good for about 40,000 BTU/hr at Beantown's +12F outside design temp, serving a load that's probably less than 25,000 BTU/hr. It's not clear why you need a
pair 12RLF slim ducts and 4 separate zones? I could heat my 2400' house in Worcester at -5F with that much equipment!
I suspect the 2-ton
AOU24RLXFZH and a single
12RLF ducted zone and a pair of 7RLF ductless heads would be better matched to your loads. The 7RLF heads are probably oversized for the individual bedroom loads though, and would cycle on/off rather than modulate, but a single 12RLF is good for 15,000 BTU/hr or better @ +12F.
Code may not demand a Manual-J when the mini-splits are not your sole source of heat, but getting the most comfort and efficiency out of the mini-splits demands it.
A typical 1920s bedroom in a house that has retrofitted insulation and storm windows or double-panes would have a load of less than 3000 BTU/hr @ +12F, which is about the MINIMUM out of a 7RLF head. When it's warmer than that out it'll be cycling, not modulating. The key is to have it cycle as little as possible, and at it's lowest speed, which is dependent on how many other zones are calling for heat.
The minimum modulated output of a 12RLF is 3100 BTU/hr @ +47F, the minimum modulated output of either multi-split is 6100 BTU/hr @ +47F. If (as I expect is the case) your whole house heat load at +12F is about 20,000 BTU/hr, the whole house heat load at +47F is going to come in at about 7000 BTU/hr, so the non-bedroom parts would have load of maybe 6K, or roughly at the compressor's minimum modulation at that temp. With two 12RLFs running they'll be forcing each other into a less efficient non-modulating on/off cycling mode whenever it's above freezing outside, but with just one it would be able to run pretty much continuous operation at least until the temps were in the mid-40s.
When only one of the 7RLF is calling for heat it's forced to take the full 6100 BTU/hr out of the compressor, but when more than one zone is calling it can throttle back to a more efficient and more comfortable blower speed. If you have too many zones, each with a minimum modulation of 3100 BTU/hr you can't count on the overlap- they'll all be cycling on/off. So to get any efficiency out of the 7RLFs your are better off with just ONE mini-duct cassette for the rest of the house, sized so that it's running almost continuously.
A pair of ducted systems for the first floor would be a mistake- it's less efficient, less modulating comfort, and would force the 7RLFs to run at a higher/less efficient speed much of the time. To get reasonable efficiency out of the system it MUST have a reasonable load, and if the zone cassettes are ALL oversized for their zone loads the performance will be pretty lousy.
Seriously, short of a Manual-J, at the very least make yourself a spreadsheet and run a room-by-room, zone by zone I=B=R load calculation on your house.
Keep in mind that the 12RLFCD can deliver more than 16,000 BTU/hr at the HSPF testing temperature of +17F, and even if it doesn't quite cover 100% of the load at +12F it'll cover most of it. I'd have to consult the engineering manual if it's kosher to hang an 18RLFCD and a pair of 7RLFs on the 24K compressor. If that combination of equipent works and the calculated load for the first floor is much over 15,000 BTU/hr @+12F it might be a better choice than a single 12RLFCD. But there's just no f'in' way the heat load for the first floor is anywhere near the combined 30,000 BTU/hr output of a pair of 12RLFCDs (at least not with the windows and doors closed!
) .