Is this UPC or IPC?
For the UPC you have a problem because the WC needs a 2" vent path to the roof. So the lav dry vent needs to be 2" and can't connect to the 1.5" dry vent you show upstairs on the kitchen sink. IPC only requires a 1.5" dry vent for the WC, so this is not a problem.
Additional requirements for the UPC (a) the distance from the shower trap to the combo where it joins the lav is at most 60", and the fall at most 2" and (b) the distance along the pipe from the closet flange to the wye where the WC drain joins the lav and shower is at most 72".
The IPC gives you more flexibility--you may join the lav drain to the WC first, rather than having to bring it around to the shower drain, and the shower trap arm may be 8' long (although that requires a perfect 1/4" per foot slope). And the WC fixture drain length is unlimited.
Cheers, Wayne