I'm struggling to lay out my drains and vent for a second floor bathroom. The current layout is offset to the left. The new bowls are 30" apart. My new vanity has bowls centered where the green lines are drawn. Basically on top of the studs. What are my best options:
Option 1: Connect a drain to the existing using a wye. I think this is too much of a drop, more than 1 diameter, and would not be correct
Option 2: Stack 2 san tees. I'm still concerned about the drop but many tell me this is ok. And then connect to the current vent higher above the counter.
Option three: Dog Leg the drain over so it's centered between the sink and use a cross san tee or double utility tee. And then go up from there and reconnect to the vent.
The red rectangles represent the inside of the cabinet where I have access. The paper rectangles taped to the wall are just the current cutout in the back of the cabinet.
 

Attachments

  • OPTION 1.png
    OPTION 1.png
    665.6 KB · Views: 56
  • OPTION 2.png
    OPTION 2.png
    686.4 KB · Views: 57
  • option3.png
    option3.png
    726.2 KB · Views: 66

WorthFlorida

New chemo regiment started Aug 20th.
Messages
5,990
Solutions
1
Reaction score
1,069
Points
113
Location
Orlando, 32828
Option 3. This my home done by a plumber. I have an AAV for venting as was the single bowl vanity.

1722386413873.jpeg
 

Breplum

Licensed plumbing contractor
Messages
2,169
Reaction score
908
Points
113
Location
San Francisco Bay Area
In "Worth's" illustration, a double tee is used, which is not to code. The fitting is supposed to be a double fixture tee.
shopping

It is required to have a 2" drain to meet code for two lavs. Will 1-1/2" work? Yes, especially with low flow faucets.
 

WorthFlorida

New chemo regiment started Aug 20th.
Messages
5,990
Solutions
1
Reaction score
1,069
Points
113
Location
Orlando, 32828
In "Worth's" illustration, a double tee is used, which is not to code. The fitting is supposed to be a double fixture tee. It is required to have a 2" drain to meet code for two lavs. Will 1-1/2" work? Yes, especially with low flow faucets.
I noticed it when the plumber was here. I could not find one in stock anywhere
in PVC. But two small sinks at 1.5" I have no drain issues. If it became an issue I can pull the vanity out as I did not replace the dry wall to allow air for the AAV. I many times I fill one sink up and let it drain. Faucets are 1.25 gallon and the smallest sinks Kohler makes. I understand why a double fixture tee is needed.

I had a tiler scheduled and needed a tub installed with a new rough in valve and covert to a double sink.
 
Last edited:
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks