Theres either a problem with the wiring or programming. Ecobee under furnaces/ boiler - section on fans ,fan should operated by ecobee.
The original actuator worked for over 4 years. when I put the original actuator back (with same wiring) it works without clicking.

The problem is the new actuator. See
 

Fitter30

Well-Known Member
Messages
5,515
Reaction score
1,112
Points
113
Location
Peace valley missouri
After looking at that video thats one reason had you pull the stat and jump R to W to take the stat out of the picture but you wrote valve didn't open. The work around is using a 24v relay have the ecobee power it and a separate transformer to power the valve switch by n.o. contact.
 