Oh, one more important point. While the IPC does not require it, the IRC's plumbing section P3108.1 requires that on a horizontal wet vent each fixture connect horizontally to the wet vent. And it appears that Pennsylvania has adopted the plumbing sections of the IRC, rather than just the IPC, without providing the option to use the IPC instead.
Explore a searchable database of US construction and building code. Code regulations are consolidated by state and city for easier navigation.
up.codes
Explore a searchable database of US construction and building code. Code regulations are consolidated by state and city for easier navigation.
up.codes
So, you can't join the WC to the top of the horizontal wet vent as shown. Your options all require more width in the joist bay (if this is in a framed floor) than your drawing would:
1) Put a horizontal wye in the 3" horizontal wet vent, and connect the WC to the branch inlet of the wye with a closet bend.
2) Use the middle vent riser in your diagram to dry vent the WC. To do this you'd need to keep the tub and shower separate from and parallel to the WC drain, and only join them into 3" line downstream of the middle vent riser takeoff.
Cheers, Wayne