Based on the date code my Sta-rite VIP III well pump controller, I have a ~34 year old well pump. The controller is model VIP4D02-07, which from what I gather would correspond to a 3/4HP well pump. The well record shows total bore depth of 155 ft, and a static water level ~88 feet below grade in 1965, however, I live in an area where the water table appears to have risen significantly with the departure of manufacturing since then. Based on the well my neighbor just drilled ~100' from my well, the static level is probably more like 63 feet below grade currently. Drawdown when pumping was only 2' when pumping at 25gpm for 24HRS when the well was drilled in 1965. When the pump kicks in at 30 psi and I have a hose bib faucet wide open with a short 10' x 5/8" garden hose attached to it, I am only getting roughly 5 GPM from the running pump, with the pressure stabilizing at ~38 psi. Based on some Franklin pump curves I looked at, I'd expect more gpm for a 3/4HP pump with a Total dynamic head ~158 ft at 5 gmp for my system (assuming total equivalent pipe length of ~200' of 1" steel pipe at the end of the hose and the 38 psi at the pressure tank). For the depth of my well, I'd figure a 3/4HP pump would be an original 10 or 15 GPM pump, and I'd expect to get more like 10 GPM vs. what I observed.
Wondering if I should consider replacing this pump now based on the above? Or if I am possibly overlooking something in figuring what the flow rate should be. Also, is this amount of reduction in flow typical for an old pump?