Why is my boiler pressure getting so high?
I have a 2 pipe hot water system with baseboard convectors. We recently drained the system to install some additional radiators. I like to keep the pressure at around 25 psi, in this building the top floor is about 40ish feet above the boiler. However a little extra pressure seems to prevent the top floor radiators from becoming airbound. Pipes are sweat copper and boiler is a navien NHB not a combi. There is an indirect water heater zone.
So we refill the system yesterday and the boiler reports 30 psi. I call my installer and he says it's probably a defective pressure sensor in the boiler, and to check pressure with a gauge. I have a brand new gauge, and I check the pressure at the purge valve - 17psi. Just when I'm thinking all is fine, the T&P relief valve on the boiler piping opens, it's a 30psi unit, and the boiler is reading 33 psi. Now I'm suspecting my gauge is not right, new gauge ordered(do i need to calibrate the gauge?).
So I do the following. I drain the system down, pump the expansion tank to 25 psi. There's no evidence of damage to the tank, it's holding air as far as I can see. Now I refill, purge, and bleed the system as best I can. I adjust the PRV for approximately 22 psi(as read on the boiler) with the system cold. It's a taco cast iron prv with a max setting of 25psi. Next I turn on the heat and wait for the boiler to read 180 degrees. The pressure is around 25 and holds for a few hours, I am happy. I come back this morning, the pressure is 32. Do I need to replace the expansion tank? The PRV? Also the system ran fine for about 4 years with this configuration.
What on earth is going on?
Thanks,
DIY
I have a 2 pipe hot water system with baseboard convectors. We recently drained the system to install some additional radiators. I like to keep the pressure at around 25 psi, in this building the top floor is about 40ish feet above the boiler. However a little extra pressure seems to prevent the top floor radiators from becoming airbound. Pipes are sweat copper and boiler is a navien NHB not a combi. There is an indirect water heater zone.
So we refill the system yesterday and the boiler reports 30 psi. I call my installer and he says it's probably a defective pressure sensor in the boiler, and to check pressure with a gauge. I have a brand new gauge, and I check the pressure at the purge valve - 17psi. Just when I'm thinking all is fine, the T&P relief valve on the boiler piping opens, it's a 30psi unit, and the boiler is reading 33 psi. Now I'm suspecting my gauge is not right, new gauge ordered(do i need to calibrate the gauge?).
So I do the following. I drain the system down, pump the expansion tank to 25 psi. There's no evidence of damage to the tank, it's holding air as far as I can see. Now I refill, purge, and bleed the system as best I can. I adjust the PRV for approximately 22 psi(as read on the boiler) with the system cold. It's a taco cast iron prv with a max setting of 25psi. Next I turn on the heat and wait for the boiler to read 180 degrees. The pressure is around 25 and holds for a few hours, I am happy. I come back this morning, the pressure is 32. Do I need to replace the expansion tank? The PRV? Also the system ran fine for about 4 years with this configuration.
What on earth is going on?
Thanks,
DIY