I'd like to make sure I am interpretting this correctly before chatting with the inspector. I'm replacing a bunch of old galvenized with PEX and planned to do a homerun system for a variety of reasons. I had a few questions.
1) Does the below (120-8-2-2) just mean the stub out needs to be within 30" of say a faucet. For example, a 20ft run to a lav with a 24in SS hose from the valve to the faucet?
2) The table below appears to call for 3/4 inch for a shower, but only 1/2 for a bathtub. That doesn't seem logical - do others interpret it that way.
1.
1) Does the below (120-8-2-2) just mean the stub out needs to be within 30" of say a faucet. For example, a 20ft run to a lav with a 24in SS hose from the valve to the faucet?
2) The table below appears to call for 3/4 inch for a shower, but only 1/2 for a bathtub. That doesn't seem logical - do others interpret it that way.
120: Water Supply and Distribution, Kentucky State Plumbing Code | UpCodes
UpCodes offers a consolidated resource of construction and building code grouped by jurisdiction
up.codes
1.
- The minimum size water service from the property line to the water heater shall be three-fourths (3/4) inch.
- The hot and cold water piping shall extend three-fourths (3/4) inch in size to the first fixture branch.
- More than three (3), one-half (1/2) inch fixture branches shall not be supplied from a one-half (1/2) inch pipe.
- The schedule in this subsection shall be used for sizing the water supply piping to a fixture.
- The branch pipe to a fixture shall terminate not more than thirty (30) inches from the point of connection to the fixture and shall be brought to the floor or wall adjacent to the fixture.
Fixture Branches | Nominal Pipe Size (Inches) |
Bath tubs | 1/2 |
Combination sink and tray | 1/2 |
Lavatory | 1/2 |
Water closet (tank type) | 1/2 |
Hot water boilers | 3/4 |
Wall hydrant | 1/2 |
Shower (single head) | 3/4 |