First post, but have tried everything else I could find with no solution, so here goes.
We have a Ducane 95G1UH/DF Propane Furnace. Installed in 2015 and no real issues since then.
Recently, the furnace works fine, but the indicator light gives three flashes. After 12 minutes or so, the furnace shuts down and gives 6 flashes. Power cycling restarts the process. It'll behave this way for a few days, and then work fine for a while (sometimes weeks).
3 flashes: Pressure switch open with inducer on
6 flashes: Pressure switch cycle lockout
If I bypass the pressure switch (after the inducer starts), the furnace runs fine and no indicator lights.
I tested the pressure switch and confirmed it switches from open to closed after inducer turns on (multimeter goes from OL to continuity, Ohms go from OL to 1.2 and voltage goes from 0 volts to 26 volts).
I pulled all tubes from switch and confirmed they were in good shape with no cracks, had no obstructions and made good seals when replaced.
I checked the condensate trap on the flue and pulled that tube. It did have a tablespoon of water that drained out and some gunk collected around the filter. I cleaned it up and confirmed the tube and filter were clear.
I check all the condensate lines and confirmed they were clear and draining properly.
I checked the flue from the roof. Seems to be venting well and was clear all the way down to the turn in the PVC.
I did notice that the inducer motor seems to get rather hot, but seems to be running fine.
So I'm not sure what else to check and looking for some guidance. What did I overlook or miss? I'm obviously not a professional, but currently unemployed so rich on time (if not a little poor on cash haha) hence the DIY attempt. I appreciate any suggestions!
We have a Ducane 95G1UH/DF Propane Furnace. Installed in 2015 and no real issues since then.
Recently, the furnace works fine, but the indicator light gives three flashes. After 12 minutes or so, the furnace shuts down and gives 6 flashes. Power cycling restarts the process. It'll behave this way for a few days, and then work fine for a while (sometimes weeks).
3 flashes: Pressure switch open with inducer on
6 flashes: Pressure switch cycle lockout
If I bypass the pressure switch (after the inducer starts), the furnace runs fine and no indicator lights.
I tested the pressure switch and confirmed it switches from open to closed after inducer turns on (multimeter goes from OL to continuity, Ohms go from OL to 1.2 and voltage goes from 0 volts to 26 volts).
I pulled all tubes from switch and confirmed they were in good shape with no cracks, had no obstructions and made good seals when replaced.
I checked the condensate trap on the flue and pulled that tube. It did have a tablespoon of water that drained out and some gunk collected around the filter. I cleaned it up and confirmed the tube and filter were clear.
I check all the condensate lines and confirmed they were clear and draining properly.
I checked the flue from the roof. Seems to be venting well and was clear all the way down to the turn in the PVC.
I did notice that the inducer motor seems to get rather hot, but seems to be running fine.
So I'm not sure what else to check and looking for some guidance. What did I overlook or miss? I'm obviously not a professional, but currently unemployed so rich on time (if not a little poor on cash haha) hence the DIY attempt. I appreciate any suggestions!