I have been dealing with a chattering pressure switch issue on pump cut-in and can't seem to resolve it, yet...
It's a 30-50 switch, currently set at 35-55psi. The setup has a 2gal Well-X-Trol just next to the pump and the main Flowtec tank sits about 30' directly to the left of the picture I attached. It has functioned just fine for many years until recently.
When the pump cuts-in, the switch will chatter 3-4 times as the pressure gauge bounces wildly before it settles in. A back pressure issue, I would assume.
What I have done:
a) Removed the pressure from the system and made sure the air pressure in both tanks was set at 32-33psi.
b) Replaced the pressure switch with a new unit. Contacts on the old one looked a little burnt.
c) Removed and inspected the tubing from the regulator to the switch - all clear.
The issue prevails.
One thing I noticed is that when the pump achieves cut-out pressure, the corresponding pressure in the main Flowtec tank increases as expected, however, the pressure in the small Well-X-Trol remains at 32-33psi. Is this normal? It doesn't seem so, but I am not sure and that is why I am seeking advise from you pros!
Thank you!
I have been dealing with a chattering pressure switch issue on pump cut-in and can't seem to resolve it, yet...
It's a 30-50 switch, currently set at 35-55psi. The setup has a 2gal Well-X-Trol just next to the pump and the main Flowtec tank sits about 30' directly to the left of the picture I attached. It has functioned just fine for many years until recently.
When the pump cuts-in, the switch will chatter 3-4 times as the pressure gauge bounces wildly before it settles in. A back pressure issue, I would assume.
What I have done:
a) Removed the pressure from the system and made sure the air pressure in both tanks was set at 32-33psi.
b) Replaced the pressure switch with a new unit. Contacts on the old one looked a little burnt.
c) Removed and inspected the tubing from the regulator to the switch - all clear.
The issue prevails.
One thing I noticed is that when the pump achieves cut-out pressure, the corresponding pressure in the main Flowtec tank increases as expected, however, the pressure in the small Well-X-Trol remains at 32-33psi. Is this normal? It doesn't seem so, but I am not sure and that is why I am seeking advise from you pros!
Thank you!