Basement sink vent

Users who are viewing this thread

Mikept

DIY Senior Member
Messages
154
Reaction score
0
Points
16
Location
CT
I'm finally going to fix that abs washer standpipe in the basement at my parents house. Its in a cleanout, 1.5" and on the wrong side of stack. I know to clamp cast iron before snapping and I want to fix with pvc .

I`m also planning for a utility sink in the future and not sure the best way to vent so i should figure that out before i cut the stack.

The concrete wall where the washer standpipe will be moved to is 4' behind the stack.
The sink would be 6' down the wall from the standpipe , combined 10' from the stack. Read the IPC and thought of a few different ways to vent the sink the extra 2'.

A: single 2" pipe. sink trap behind dryer so a 2' trap arm; 4' to ell/standpipe wye. 4' to stack.

B: single 3" pipe so 6' to ell/standpipe wye. 4' to stack.

C: double 2" pipes so combined waste vent the sink; 6' to ell, 4' to stack. another 4' pipe for standpipe to stack.

Am I reading the IPC right? I dont want to mess with walls on the above floors or an AAV.

20150404_124853.jpg
 
Last edited:

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
That looks like a waste/soil stack and can not be used for venting basement fixtures. You need to look around to find a vent.
 