One of the pressure switches went bad a few years back so they cut them out of the circuit. I don’t see a time delay - the y1 (former y2 when wired wrong) goes straight to the contactor. But it’s been wired so y2 was that wire that connected to the contactor and y1 was going to the cs. I changed it so y1 is now correct. I think it’s always been wired wrong. But even with y1 correct, when it kicks on it energizes both y1 and Y2. I really think that that y1 should be alone on one side of the contactor and y2 and the common on the other. I think when y1 is getting 24v it is always energizing y2 through as they are both connected to the same side of the contactor.
I moved it so it matches the following:
Y1 goes straight to the right side of the contactor. Y2 goes to cs and comes back to the left side of the contactor. Common goes to the left side.
I can’t get a pick of the cs - it’s at the very bottom of the compressor.
I’ve nervous to turn it on though! Lol! I think it should work this way…can I try it or do you see an issue with it?
Ok - so I got brave….
I wired it the way I described. Y1 goes straight to right side of contactor. There are no pressure switches or delays. Common goes straight to left side. Y2 goes to cs and the red wire comes back to the same side as the common.
Turned it on. Compressor pulled 9.5 amps in stage 1. When it kicked to stage 2 it started pulling 13.5 amps! So, that should be right, right? I think this id how it is supposed to go. It’s just hard for me to believe it’s been wired wrong all these years.
My only worry is that when they took out the switches due to them failing a few years back that maybe they purposely wired it so it never went into the higher stage?? Is it safe to not have the time delay and switches?