    Default Is this legal, or will it at least work? Bath rough-in

    I did this a year ago and just went back and looked at the pictures. Should I have put a long sweep 90 on the toilet going to the main line? I forgot what my reasoning was at the time but it probably wouldn't have fit and I didn't want to do any more digging...

    Name:  Grover house rough in 008.jpg
Views: 336
Size:  55.6 KB

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    What is that 2" elbow in the background? You managed to take the picture precisely so it was obscured. If that is for a tub or shower, then it IS both illegal and will not work. IF you had used a "closet bend" it would have had an even "sharper bend" than your elbow so it is okay, but the sanitary tee it goes into is NOT. Your toilet vent is also NOT according to codes. According to your picture, you have a 2x6 sticking INTO the 2" vertical pipe at the left. How did you do that? as fpr the second part, "Will it work", almost every cockamammy idea DIYers come up with "will work" which is why they want to do it their way. The questions then become "how well will it work and for how long".
    Last edited by hj; 12-08-2012 at 09:36 AM.
    Licensed residential and commercial plumber

  3. #3
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    Here's another picture. That 2 inch elbow in the background comes up from the main drain line and 90s over to a shower drain. The 2x6 is an old wall that got cut out and replaced. The 2 inch vent pipe goes up through the wall. So what's the worst case scenario and how should it be fixed?? Here's another picture.

    Name:  Easter 2011 013.jpg
Views: 299
Size:  68.1 KB

  4. #4
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    The reason I went with the 2 inch vent is because I wanted to make the wall a 2x4 wall. Plumber said it was okay to have the vent pipe 1/2 diameter of the toilet pipe. Probably should have done 3 inch for the toilet, but the existing one was 4 inch so I replaced what was there.

  5. #5
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by djlazar View Post
    I did this a year ago and just went back and looked at the pictures. Should I have put a long sweep 90 on the toilet going to the main line?
    Just a fellow DIYer here, but I believe you should have used a double-wye where you have that sweep 90, and then a 45 or whatever to get the toilet line over to it. A sanitary tee should never be used horizontally, and the one you have there for the toilet line could be troublesome since solids can stick at the turn and you have no cross-flow to help keep it clear.
    Last edited by leejosepho; 12-08-2012 at 05:58 PM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  6. #6
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    I see your point about the tee. I didn't do my homework before doing that. That would be easy to dig back up. What about that shower drain? It comes up from the main pipe about a foot then 90s over to the bathtub p trap about 4 feet over. Is that going to cause me problems draining? (I haven't used the house yet)

  7. #7
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    While I agree that the sanitary tee should not be used on it's side or back, (wye fittings are always used on horizontal) I would be more concerned about the improper/lack of venting. If that is a dry vent, it will be clogged the first time there is the slightest backup. The shower/tub is also not vented. All vents must rise vertically until they are at least 6" above the flood rim of the highest fixture served. I am sorry to tell you that the best thing you could do is cut all of that plumbing out and start over.

    Here is a nice link to Bert Polk's plumbing tips- http://www.co.lincoln.or.us/planning...mbingguide.pdf
    Last edited by cacher_chick; 12-09-2012 at 08:51 AM.

  8. #8
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    That 2 inch is actually a drain for a sink as well as the vent. Does that make a difference? And what about the tub? The bathtub has that little vent thing on it. I thought that was the vent for the tub.

  9. #9
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    The toilet can be wet vented through the lavatory drain, but bend at the bottom of the vertical stack should be a long-turn 90 or a pair of 45s. The connection of the wet vent to the main line should made with a wye which should be downstream of the water closet.

    The tub must have a vent located downstream of the trap. The tub's overflow is not a vent, it is an overflow.

  10. #10
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    How far downstream of the trap is it supposed to be vented? (i could have just googled it but it's easier to just ask)

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,448

    Default

    The better question is "how far away from the trap can the vent be?". That depends on the diameter of the pipe - the larger the pipe, the further away the vent can be. Ideally, the vent is at the point where the trap arm enters the drain, but there is some leaway depending on the pipe diameter. The vent must come off the trap arm before it turns down to vertical AND within the max distance.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    Okay, did my homework, can't find it. With a 2 inch drain pipe, how far away from the trap can the vent be? It goes from horizontal to vertical after about 2 1/2 to 3 feet away from the trap right now.
    Here's my plan, someone tell me if there is a problem with this. I plan on cutting out the 90 where the tub drain goes from horizontal to vertical and adding a 2x2x1 1/2 fitting, then taking the vent pipe up about a foot, put a 90, and sloping down a little and tying into the 2 inch main vent that goes up to the sink. I'm sure that's not code but I don't want to cut out any sheetrock.

  13. #13
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,448

    Default

    I think with a 2" pipe, it has to be within 5', so IF I'm correct, that part is okay. BUT, a vent, like a drain must not have a place where moisture could accumulate (i.e., it CANNOT go up/down/up - it must contain a continuous path for moisture to flow should any get into that pipe) plus, code says it must go at least 6" above any other drains in that run OR 42" above the floor, whichever is higher before it can go horizontal. Any rain, snowmelt, condensation, etc. that gets into that pipe where it goes back down for a bit will accumulate, block it off, and make it inoperative. Sometimes, you just have to bite the bullet if you want it done right.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  14. #14
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    Quote Originally Posted by djlazar View Post
    Okay, did my homework, can't find it. With a 2 inch drain pipe, how far away from the trap can the vent be?

    It's funny, because I just googled "Oklahoma Plumbing Code" and the first site listed has a PDF of the entire code. In the 2006 IPC, venting is covered in chapter 9, and the information you are looking for is in section 906 & table 906.1.

    I suggest you spend some time reading the entire chapter. It's fairly clear as to what you have to do.
    Last edited by cacher_chick; 12-15-2012 at 09:59 AM. Reason: typo

  15. #15
    Electrician djlazar's Avatar
    Join Date
    Apr 2007
    Location
    Norman, OK
    Posts
    16

    Default

    I know what the code book says. Don't really give a damn about the code book. I was going to go up about a foot, then 90 over (with a slope) to the vent for the toilet/sink. I was just wondering if anyone saw a potential problem, other than the drain clogging and the vent getting full of water during a flood, in which case a vent full of water is the least of my problems. This is a house, not a commercial project.

    Mike Holmes may "do it right" but he has sponsors and an unlimited budget. Honestly, does anyone on here do plumbing for a living? The most helpful posts I've read on here are from other diy'ers. Out of our entire local, I know of 1 guy that quotes the code book, other than 3rd year apprentices that want to show off how much they've learned.

Similar Threads

  1. Basement Rough In- how much re-work?
    By aschmidt48 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-10-2011, 07:36 PM
  2. Rough Cost Estimate: Basement Wet Bar and Bathroom Work
    By bucky in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 08-13-2011, 06:17 PM
  3. Does the rough-in still work?
    By Ian Gills in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 01-06-2009, 12:30 PM
  4. Will this rough-in work?
    By imunwell2 in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 10-17-2007, 07:18 AM
  5. Will a 12" Rough-in work for me?
    By Mary G in forum Toilet Forum discussions
    Replies: 2
    Last Post: 10-06-2007, 01:53 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •