Didn't see a place for an intro. I've been in construction as an electrician for 25+ years. Of course I've done all sorts of trade work for myself over the years. Currently on a full basement blowout and remodel and looking to confirm my DWV layout......

Hopefully this quick computer sketch makes some kind of sense. The existing upstairs bath group is vented up and drops into the main exiting the house. Next upstream is the reconnect for the upstair kitchen sink and washer, also venting up or connecting with the main stack in the attic. Next to connect below grade is the wye for the basement washer and lav, this can vent up in 2" though wondering if an AAV would be acceptable. Next upstream is an W.C. branch then a 2" wye to vent the W.C. then a wye for a tub and on to a riser for a cleanout reducer to 2" vent up. Also wondering if an AAV would be acceptable there. If needed I may be able to take those up through the attic......
The 1st floor fixtures all drop to the 3" below grade ahead of the basement fixtures.
How's it look?
 

Attachments

  • IMG_0007.png
    IMG_0007.png
    87.3 KB · Views: 88
Last edited:

Reach4

Well-Known Member
Messages
38,903
Reaction score
4,437
Points
113
Location
IL
Denver uses IPC. https://up.codes/viewer/denver/ipc-2021
The most common way to vent a toilet is to use a horizontal wet vent. A big example, which covers two bathrooms, is on the bottom of page 12 of https://www.iccsafe.org/wp-content/uploads/20-18927_GR_2021_Plumbing_Venting_Brochure.pdf

An important point is that horizontal wet venting only applies to bathrooms, and that if you inject something else, such as a laundry standpipe or kitchen drainage, horizontal wet venting is done.

If you look at your project with this in mind, you will probably ease your plans.
 

mtne

Electrician
Messages
6
Reaction score
0
Points
1
Location
Denver, CO
Website
www.advrider.com
Denver uses IPC. https://up.codes/viewer/denver/ipc-2021
The most common way to vent a toilet is to use a horizontal wet vent. A big example, which covers two bathrooms, is on the bottom of page 12 of https://www.iccsafe.org/wp-content/uploads/20-18927_GR_2021_Plumbing_Venting_Brochure.pdf

An important point is that horizontal wet venting only applies to bathrooms, and that if you inject something else, such as a laundry standpipe or kitchen drainage, horizontal wet venting is done.

If you look at your project with this in mind, you will probably ease your plans.
Thanks,

so I see the separate vent allowing a dry vent isn’t needed and as there’s no kitchen or laundry above, wet vent standards will suffice. Is and AAV acceptable for that branch?
 

Reach4

Well-Known Member
Messages
38,903
Reaction score
4,437
Points
113
Location
IL
Replace "above" with "above or downstream-from".

You need a vent, which could be an AAV, for each lavatory.
 