It might be that the connection between the neutral bars is bad. You would not be having the symptoms you listed because of a loose ground.
That's what the problem was. I took off the connector between neutrals and it was smoked. I cleaned it up and put it back together and it is working perfect. Thanks.
 

Travis Hall

New Member
Messages
13
Reaction score
0
Points
1
Location
Kentucky
The problem was a loose connection on the connector for the neutral bars. It's fixed now. Thanks for all the help.
 

Widgit Maker

Member
Messages
173
Reaction score
21
Points
18
Location
Alexandria, Virginia
Suggest that you turn off all those arc fault breakers and do you voltage check again. I would remove the breakers to do the checks. In other words, I suspect you have a faulty arc fault breaker that is putting voltage on the neutral.

The problem was a loose connection on the connector for the neutral bars. It's fixed now. Thanks for all the help.
Want to bet? A loose connection to the neutral buss would not put 250 volts between a hot and a neutral.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Suggest that you turn off all those arc fault breakers and do you voltage check again. I would remove the breakers to do the checks. In other words, I suspect you have a faulty arc fault breaker that is putting voltage on the neutral.


Want to bet? A loose connection to the neutral buss would not put 250 volts between a hot and a neutral.
If the neutral is open, any 240vac circuit could give you weird voltages through the panel when on (say a WH, or furnace, stove, etc.). In the panel, neutral and ground are connected...if there was a connection from the hot side, you'd normally either have a fire, or trip a breaker.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Huh? The voltage between an open neutral bus and a hot could vary between 0 and 240V, depending on the 120V loads on both hots.

It would depend if the open neutral was on the line or load side.
 