Hondo

New Member
Messages
1
Reaction score
0
Points
0
Location
70435
I am having issues wiring up a new Panasonic FV-0511VHL1. I removed an old vent/heat/light combo unit controlled by 3 single-pull switches. For me, the wiring diagram directions are confusing and do not match my current switch layout. Does anyone have any experience with this? I have attached images of the old junction at the unit and images of the new. I know the ground wires go together, the white wires go together, and blue wires for the light go together. I do not need the night light function. It gets confusing on how to hook up the fan and heater. Any advice?
 

Attachments

  • 20240920_111845 (1).jpg
    20240920_111845 (1).jpg
    105.3 KB · Views: 275
  • 20240920_134627.jpg
    20240920_134627.jpg
    94.3 KB · Views: 289
  • Screenshot 2024-09-20 150629.png
    Screenshot 2024-09-20 150629.png
    59.8 KB · Views: 467

wwhitney

In the Trades
Messages
7,251
Reaction score
2,067
Points
113
Location
Berkeley, CA
If the previous setup had 3 single pole switches, then that presumably means you only have 4 conductors (ignoring grounds) from the switch location to the fan location? Neutral and 3 switched hots?

If so, and you're happy to abandon the night light functionality, replacement is straightforward. Just cap off the night light connection on the unit with a wire nut. Then ground goes to ground, the supply neutral goes to both unit neutrals, and each of the 3 switched hots goes to its respective function, which the wiring diagram is calling calling Live (Light), Live(Vent), Live (Heat).

Cheers, Wayne
 