Instaling Navien NPE-A on house with no dedicated recirc line

Users who are viewing this thread

JWplumbing

New Member
Messages
11
Reaction score
0
Points
1
Location
Texas
Installing navien npe-a on house without dedicated recirc. So I want to have a recirc system. Does the npe-a need a dedicated recirc? It is a possibility as we are doing a remodel… I know the npe- a has an internal recirc but what do I do to make this work the best and most efficiently?
 

Breplum

Licensed plumbing contractor
Messages
1,940
Reaction score
778
Points
113
Location
San Francisco Bay Area
Plan on installing a full recirc. loop. If PEX, then 3/4" is required.
The most efficient system is to utilize the Hot Button system and have all relevant spots trigger the pump only when desired.
Only licensed professionals should be installing.
 