A lot of times the trip on low pressure is caused by too much air in the pressure tank. Anytime the bladder hits the bottom of the tank, the low pressure will trip off. So no matter what pressure it is set to shut off, a low pressure “safety switch” will always go off at exactly the same pressure as the air charge in a bladder tank. Without a bladder style tank, sometimes the switch is just mounted too far from the pressure tank.
However, low-pressure switches are supposed to go off when demand exceeds supply, and that is what they do. Yes it is a pain to crawl under the house to reset a pressure switch. Yes it is hard to tell the wife she only has a 5 GPM pump, and so she can only fill her tube with the fill valve ½ way open. Yes it is agonizing to explain to the brother in law over the phone how to crawl under the house to reset the pressure switch after a power outage or after she “overfilled” the tub. But those little levers on the side of that switch have saved countless pumps from running when there is no water to pump. The only time they don’t work on a dry well application is when no water is actually being used, and the pump runs dry while trying to refill the pressure tank.
I use the Allen Bradley 836 as a low pressure kill for more technical pump systems. It is infinitely adjustable to the pressure and bandwidth you want to work at. However, it doesn’t have the little lever to reset with, and it can’t do both jobs with one switch. I have to use one switch to turn the pump on/off at the regular 90/100, and wire it in combination with another switch so I can set a low pressure shut down for 60 PSI. This way it takes two pressure switches for each pump, and you need a way to bypass the low-pressure switch just to get the system up to 60 PSI. I use a push and hold button to bypass the low-pressure switch until the system is charged.
As I said earlier, there are situations where a low-pressure kill will not shut the system off when the pump runs dry. For that reason I use a Dry Well device like the Cycle Sensor. These devices look at amp draw instead of pressure. They can tell if the pump is running dry under any condition.
I use the low-pressure kill to prevent flooding during a major line break, not for dry well protection. A line break can turn a golf course into a lake by the time someone wakes up in the morning. So a low-pressure kill is very important on larger systems.
Also when using a Cycle Sensor for Dry Well Protection, it can be set to restart automatically between 1 and 500 minutes. That way you can tell the wife to cut the tub fill in half, and wait one minute for the pump to come back on. Happy wife, happy life!