I am maintain more than a dozen homes with submersible and shallow well pumps. On two that can frequently develop low/no water I have installed low pressure cut-off swithes so that the pumps won't run continually when there is no water. My problem is that every so often when there is plenty of water available and everything is OK the low pressure cut-off kicks in for a reason I can't fully fiqure out. They will go for weeks with no problem and then cut-out and then be fine again after re-setting.
I reasoned that perhaps when the pressure is close to cut-in pressure and there is a larger than normal demand (ie. two toilets flushed at once) the pressure drop is too dramatic and bingo it cuts-out. This I can manage to duplicate but it is with the drain valve on the tank opened fully. Is there a way to adjust the cut-off pressure lower than factory setting to overcome this problem? I am using FSG2040 (Sq D) switches.
Thanks to anyone who can help. Sq. D has no help that I can find.
I reasoned that perhaps when the pressure is close to cut-in pressure and there is a larger than normal demand (ie. two toilets flushed at once) the pressure drop is too dramatic and bingo it cuts-out. This I can manage to duplicate but it is with the drain valve on the tank opened fully. Is there a way to adjust the cut-off pressure lower than factory setting to overcome this problem? I am using FSG2040 (Sq D) switches.
Thanks to anyone who can help. Sq. D has no help that I can find.