    Default PRV leaking frm boiler

    I have 2 pressure gauges on the system. Never read over 15psi. I have an expansion tank in place. I tested the relief valve when i flushed the boiler. I do this every fall. PRV said it is rated for 30psi. It is leaking mainly during fire up to temp (assuming as pressure builds). Never over 15 psi according to the gauges. Sounds like an end of life PRV and just replace?

  2. #2
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I replaced the valve. Old one showed a ton of corrosion inside. easy fix.

  3. #3
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    I'm guessing you didn't fix the problem. Run the boiler up to 200 and see what the gauge says then. I'll bet your expansion tank is either full (if it's a non bladder tank) or the bladder is bad. The other thing that can cause excess pressure is a leak in the tankless coil if you have one.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    Pressure gauges can become corroded too, and not indicate reality.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I used two gauges for that reason. They both read correctly. I replaced the valve and all is working just fine now.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    A bad valve should have raised the pressure "constantly", not just during startup time. Your description or diagnosis may have been faulty, but as long as what you did "seems" to have fixed it don't worry about it, but do check it periodically.
    Licensed residential and commercial plumber

  7. #7
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I think the problem here is i am talking about a relief valve not a fill valve. Maybe my terms thru you off but this is the valve off they tank to relieve excess pressure in the system.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    That would make a difference, but it would have had to be very defective to operate on the slight pressure rise that the expansion tank was compensating for.
    Licensed residential and commercial plumber

Similar Threads

  1. boiler leaking
    By suzanna in forum Boiler Forum
    Replies: 2
    Last Post: 03-15-2012, 06:20 PM
  2. Boiler Leaking what to do
    By dpw-ct in forum Boiler Forum
    Replies: 6
    Last Post: 02-25-2012, 07:06 AM
  3. New Boiler - pipes keep leaking...help
    By benj in forum Boiler Forum
    Replies: 3
    Last Post: 02-27-2011, 06:47 AM
  4. Leaking Weil MCClane Boiler
    By Kevind04 in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 02-08-2009, 01:16 PM
  5. HELP! boiler leaking everywhere
    By fast pasquale in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-11-2007, 07:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •