    OK. Which camp are you in.

    1/2 undercut for funtion (air return, etc)
    or
    1/4 -- nice and tight to flooring.

    Gonna do some door hanging and can't decide....

    Or maybe meet somewhere in the middle and do 3/8".

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Don't do it for air, if you needed it, you'd need more than the 1/2" anyway - there should be an air return doing the job in the room. A bit more is handy to help the door go over whatever might be sitting there.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,607

    Default

    quote; there should be an air return doing the job in the room

    What universe are you living in? The majority of modern homes have only one or two central returns and depend on the gap under the door for return air when the door is closed. Make a "tight gap" and then develop muscles pulling the door open when the furnace is operating.
    Licensed residential and commercial plumber

  4. #4
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    In many locations where there isn't a dedicated return in the doored-off room, jump ducts or return grilles in partition walls are required by code. It would take about a 2" door cut to meet the pressure differential requirements for a duct return path. Making the door tight WITHOUT providing a low impedance return path means you're using incidental air leakage out to the Great Outdoors to provide the return path, which takes a toll on system efficiency (and capacity).

    If you want to use the door as the return path without creating a hamster & squirrel escape route, these suckers work pretty well. They're not exactly a thing of beauty- on a par with using transom grilles or partition-wall grills. Jump ducts with ceiling grilles may be a bit less visually intrusive.

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    A 4 inch duct feeding or exhausting a room is 12.5 sq inches, a 6 inch is just over 28 sq inches. Since it is a forced supply, the passive return or make-up needs be greater. A 1 inch gap under a 34 inch door is 34 sq inches, probably adequate for return or make-up IMHO.

    I say, give the hamster freedom to roam!

  6. #6
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,714

    Default

    The max impedance spec Tamrack is working against for passive returns is 250cfm (min) @ 3 pascals pressure difference, which surely won't be met with a 1" door cut on a 34" door.

    Jump ducts are typically executed with 10" diameter flex duct, or 78-79 sq-in, which is roughly the same as a 2" door cut. Bigger rooms/volumes use 12" flex for the jump ducts. See the duct sizing and flow discussion, particularly the jump duct sizing in figure 3 here:

    http://www.buildingscience.com/docum...em-sizing-pro/

    See also: http://www.buildingscience.com/docum...return-systems

    While a 1" door cut would be much better than a tight fit, it would still be sufficient impedance to drive outdoor air infiltration.

Similar Threads

  1. Ash doors
    By Ian Gills in forum Remodel Forum & Blog
    Replies: 6
    Last Post: 01-11-2010, 07:10 PM
  2. Undercutting baseboard?
    By alt in forum Remodel Forum & Blog
    Replies: 6
    Last Post: 01-17-2008, 04:03 PM
  3. sliding doors
    By robj in forum Shower & bathtub Forum & Blog
    Replies: 6
    Last Post: 03-04-2007, 09:49 PM
  4. Non-Sliding Tub Doors?
    By az1324 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 02-20-2006, 08:09 AM
  5. Bath doors
    By Michaela521 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-10-2006, 03:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •