Did my contractor screw up? how to fix?

Users who are viewing this thread

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
Really in need of some advice here. For our kitchen remodel the contractors installed all new plumbing including a new drain pipe to the waste stack. Today as they were hooking up the sink drains, disposal, etc... I noticed the drain was higher than it should be.

IMAG0282.jpg

I'm thinking this is an issue as water will pool in the pipes and not completely drain. Assuming this is a problem how can I remedy? Going into the walls again to redo the drain is not an option. However, I have a very accessible crawlspace under the kitchen. So, is an option to add a T after the trap. The current drain would stay connected and act as the vent. The other opening of the T would go straight down into my crawlspace and tap into the same sewer line just at a lower position.

Screen shot 2011-10-28 at 11.36.06 PM.png

Any help would be very appreciated.
 
Last edited:

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
Two options to fix:

- move the connection in the wall
- use a shallower sink

The sink change may not even do it unless you have a very deep sink. By the looks of it, they set it way too high. From the angle of the pic, it looks higher than the disposal outlet, so all of that piping (and the disposal) will have water in it at all times. They messed up and should fix it for you. Although, it may be difficult at this stage.
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
A vent cannot go horizontal until it is 6 inches above the flood level (rim) of the sink.

Thanks for the reply.

I'm not sure I understand. Currently, even if the drain pipe was at the correct height, the pipe would be horizontal to the stack and not be 6 inches above rim of the sink. Does that mean I have no stack currently?

Edit... I think I understand this point.
 
Last edited:

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
Two options to fix:

- move the connection in the wall
- use a shallower sink

The sink change may not even do it unless you have a very deep sink. By the looks of it, they set it way too high. From the angle of the pic, it looks higher than the disposal outlet, so all of that piping (and the disposal) will have water in it at all times. They messed up and should fix it for you. Although, it may be difficult at this stage.

Thanks for replying. I really am trying to avoid going into the walls because everything was just done. argh. What are the consequences of just leaving it as is? Did my proposed solution diagram not get the job done?
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
So looking at my diagram again, if I just cap off the original drain (not use as vent) and just connect that drain to the stack (in blue), isn't it then still vented since I'm tapping into the stack, just at a lower position?

6290328753_434df6f332_b.jpg
 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
Blue line is no good. It creates an S-trap and effictively isn't vented.
 

Jerome2877

In the Trades
Messages
397
Reaction score
2
Points
18
Location
Vancouver Island , BC
How about removing the garburator and installing as shallow a basket strainer you can find. Relocate the Dishwasher Y to the horizontal between the 2 sinks. I can't tell from the pic if this would work but it would be close.
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
Ok, grasping for straws here. I realize none may be kosher or code but which is the lesser evil:

1. Keep existing drain as "vent" and take the new drain to sewer line in crawl space
2. Cap off the existing drain and take the new drain to sewer line in crawl space
3. Probably scoff at this one (see below) but take the drain straight down to crawlspace and put the trap there before tapping into sewer.

6290399261_279f8b1312_b.jpg
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
3. Probably scoff at this one (see below) but take the drain straight down to crawlspace and put the trap there before tapping into sewer.
I think you will find the code requires the trap to be under the sink, not the floor.

You really should have the contractor come back and make the proper repair by lowering the drain connection, and I say that as a DIYer who believes contractors should be held accountable.
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
No trap under the floor because code limits the length of the vertical drop to the trap. There are only two ways to fix this. One is to open the wall back up and move the san tee down where it belongs. The other is to abandon the whole mess, drop through the floor and use an AAV at the sink.
rate_5.jpg



The big question though is that if a "contractor" just did the work then where were the inspections both rough and final? and furthermore why not call the "contractor" back and make him fix his mistake? After all, you paid good money to have the work done.
 
Last edited by a moderator:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Let me get on my soap box here, because this general issue came up on another thread this morning. What you SHOULD have done is called in the plumber BEFORE you purchased the giant new sink, to plan out the job. He could have lowered the pipe in the wall when access was better. That is still the right thing to do, but much harder now.
rate_5.jpg


Your options are not good.. Leaving as is, you will have slow draining sink and disposer. Both the S trap and the deep trap you have proposed will not meet code.
 
Last edited by a moderator:

Gary in NJ

Member
Messages
119
Reaction score
0
Points
16
Location
NJ
You really should have the contractor come back and make the proper repair by lowering the drain connection, and I say that as a DIYer who believes contractors should be held accountable.

There's the only correct answer. The wall has to be opened.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
You can run a new drain line connection in the basement, BUT the line under the tee in the wall has to be capped so it cannot become an "alternate" drain line. The "vent" would connect right at the wall so the "horizontal" portion would be negligible. But, when I say "YOU", I mean the contractor because it is his "screwup". The way it is now the disposer will ALWAYS have water standing in it, and when the disposer is turned on it will vibrate until it pumps the water out. OBVIOUSLY, you CANNOT change to a shallower sink because that one appears to be integral with the countertop, or made from some similar material. As an aside, I, and "millions" of others in this area, have disposers AND septic tanks and they coexist without any problems.
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
Let me get on my soap box here, because this general issue came up on another thread this morning. What you SHOULD have done is called in the plumber BEFORE you purchased the giant new sink, to plan out the job. He could have lowered the pipe in the wall when access was better. That is still the right thing to do, but much harder now.

I already had my sink and disposal before he even started the job which he saw, so it's completely on him.

To be clear, the contractor hasn't left yet (haven't paid him the other 50%) and I called him out on it. He wants to work it out and we are exploring options. I'm posting here because I trust you guys a lot more than him and seeing if there are any other viable options. Cutting into the wall and cabinet, disturbing insulation, framing, etc. is what I'm trying to avoid IF I CAN. We very well may just go into the wall and do it right but just thinking out loud here. I appreciate everyone chiming in, I really do. You guys are awesome.
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
There are only two ways to fix this. One is to open the wall back up and move the san tee down where it belongs. The other is to abandon the whole mess, drop through the floor and use an AAV at the sink.

If we go the AAV route, would it work like this?

6292421754_3a4fe4a1d0_b.jpg


Did I create an S trap or does the AAV no longer make it an S trap? The AAV is still below the drain and I thought I read that's not good.
 
Last edited:

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
You can run a new drain line connection in the basement, BUT the line under the tee in the wall has to be capped so it cannot become an "alternate" drain line. The "vent" would connect right at the wall so the "horizontal" portion would be negligible.

I've read this ten times and I still don't get it. would you be so nice as to elaborate? Thanks
 

pocoloco

New Member
Messages
23
Reaction score
0
Points
0
Location
Illinois
How about removing the garburator and installing as shallow a basket strainer you can find. Relocate the Dishwasher Y to the horizontal between the 2 sinks. I can't tell from the pic if this would work but it would be close.

I'm considering this option as well. Remove disposal (don't really use it anyways) plus shallow baskets. Does the dishwasher Y have to be above the drain line since the drain line is attached at the way top of cabinet?
 
Last edited:
Top