craigw78
Unfortunately my past usage would probably be less accurate than a size based room by room calc. For the last two winters I haven't spent much time at home and kept the heat 60 degrees or lower the majority of the time without really heating my basement at all. In addition, I recently replaced my windows and entry door as well as insulated my attic. I think I will talk to the heating engineer I had over and see about getting a heat loss calc. I think that will provide the most reliable data. Using the BT = t *(Qh - qload)/(500*dT) formula it looks like my buffer tank should be 80 gallons or more. I currently have a 40 gallon tank I am thinking of adding to see if it improves my situation and if it does I will either daisy chain in another tank if that is feasible or replace it with an 80 gallon tank. Pumping shouldn’t be too much of an issue since my system currently has a Grudfos 15-42 and a 15-58.