Thread: vent stovehood into furnace exhaust

Hybrid View

  1. #1
    DIY Junior Member trcmag's Avatar
    Join Date
    Oct 2010
    Location
    Michigan
    Posts
    1

    Default vent stovehood into furnace exhaust

    my furnace and water heater vents through the roof and I need to add a exhaust for my stove top. I was wondering if I could avoid cutting a new hole in my roof and put a T in the furnace exhaust pipe and vent my stovetop through this pipe.

    The furnace and water heater are in the basement and the T would be in the ceiling in a single story house in Michigan.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    Not a good idea! You could get CO back into the house, and any grease that made it past the hood's filters, might line the furnace flue and create a grease fire. Don't think code would allow it, either. Often, people vent the range out the side, rather than the roof.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,720

    Default

    What jadnashua said- it's (rightfull) a code-disaster, and a real hazard. If the hood vent is power vented, and the furnace/water heater are atmospheric drafted (likely, if they're sharing a flue) you're guaranteed to be driving copious amounts of exhaust into the basement. Side vent it if you can, but use a decent backflow preventer no matter which way you go with it (roof or side.)

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    You really want the vent to be as short as possible. The grease filters generally work fairly well, but the warmer the air is, the more the smoke and grease can stay in suspension. Also, smoke particles tend to stick to surfaces, so the fewer elbows you have, the cleaner the vents will stay. The longer things are, the colder things get, and then you start to have problems. A grease fire in the wall is no fun! NEVER run the thing without the filters in place, and if they get replaced, make sure they are the proper ones. Clean them periodically, too!
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

Similar Threads

  1. bathroom exhaust vent sizing
    By mchristo in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 11-25-2009, 07:25 PM
  2. inline in gas furnace exhaust: what is it?
    By gdog in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 03-17-2009, 05:52 AM
  3. mouse house in the furnace exhaust
    By allycat in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 05-04-2008, 04:32 PM
  4. Can I vent my exhaust fan into a joist bay?? No moisture...
    By lithnights in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 28
    Last Post: 05-12-2006, 01:58 PM
  5. Sizing bathroom exhaust vent
    By rdtompki in forum Remodel Forum & Blog
    Replies: 4
    Last Post: 02-11-2006, 10:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •