    Default pipe size /max length of run for kitchen, Canada Code

    hello
    I have been asked to rough in a new kitchen, it has 1 double sink and a dishwasher beside it, the soil pipe is 25 to 30 feet away, I don't want to run 3 inch all the way if it isnt needed , thanks

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    Even IF 1 1/2" would be approved, there is no way I would EVER use it for anything other than a vent. I ALWAYS use 2" minimum for my drain lines.

  3. #3
    DIY Junior Member Philbert's Avatar
    Join Date
    Aug 2010
    Location
    Toronto,Ontario,Canada
    Posts
    5

    Default

    the problem I am having is that if I seach online for a quote from the npc I get a vague reference to some "complicated table" in the plumbing code book which I can acces online unless I pay for it or order a copy of the code book for a price of course,if ther is no restriction all the better, although I will likely use 2 inch anyways, ohhh the 25 to 30 foot run is a sloped run not a drop ifin that changes anything

  4. #4
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    It is not a "complicated table" at least not in the books down here. Each fixture is desinated by a number which correlates to how much water is likely to go in it. The number is called "fixture units". In the UPC, a kitchen sink is 2 FU. By the simple table, the maximum # of FU on a horizontal 1" pipe, beyond the trap arm, is ONE. So the sink needs to drain into a 2" lateral. The horizontal length ( with 1/4" per foot slope minimum) is unlimited.

  5. #5
    Journeyman & Gas Fitter Doherty Plumbing's Avatar
    Join Date
    Jun 2009
    Location
    Penticton, BC
    Posts
    810

    Default

    Quote Originally Posted by Philbert View Post
    hello
    I have been asked to rough in a new kitchen, it has 1 double sink and a dishwasher beside it, the soil pipe is 25 to 30 feet away, I don't want to run 3 inch all the way if it isnt needed , thanks
    1.5" is perfectly acceptable as long as you pick up your vent within 6'.

    I usually have a 1.5" fixture drain picked up by a 2x1.5x1.5" tee.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    I haven't seen 1.5 for kitchens since the 50's in the lower 48, not Canada though.

    Here we use a 2" waste line until the vent, and then a 1.5" trap arm. we are allowed 42" for the 1-1/2" trap arm.

    I guess the Canadian code for kitchen plumbing is pretty weak.
    Last edited by Terry; 06-29-2013 at 11:52 AM.

  7. #7
    Certified Plumber Plumber1979's Avatar
    Join Date
    Jul 2012
    Location
    Ontario
    Posts
    16

    Default

    im a plumber here in Ontario and its just fine to use 1 1/2 on a kitchen and it 5' for the vent

  8. #8

    Default

    1-1/2" is fine. trap arm max is 5' (1.5m). cleanout required on fixture drain or union p-trap. cleanouts every 20' (6m).. you'll want to make sure your slope is right to keep a kitchen sink line that long, clear of grease etc.
    secondly NPC is not what you need. you need to refer to the Ontario Building Code section 7 - Plumbing

  9. #9
    Plumber Sean Beck's Avatar
    Join Date
    Jun 2013
    Location
    Toronto, Ontario, Canada
    Posts
    46

    Default

    1.5" is permitted by code providing the vent is connected within 5ft and there is a clean out every 6m. Personally with it being a kitchen drain which is subject to grease build up, I would use 2" with cleanout every 6m.

  10. #10

    Default

    Quote Originally Posted by Philbert View Post
    the problem I am having is that if I seach online for a quote from the npc I get a vague reference to some "complicated table" in the plumbing code book which I can acces online unless I pay for it or order a copy of the code book for a price of course,if ther is no restriction all the better, although I will likely use 2 inch anyways, ohhh the 25 to 30 foot run is a sloped run not a drop ifin that changes anything
    your posts suggest that your reply to the request of the customer should have been " I don't know plumbing - perhaps you should consult a plumber "

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default pipe

    The code is a "minimum standard", and I do not know any "competent" plumber who has ever had to snake a sink drain who would use less than 2". With 3" you run into the problem of NO "self scouring" because the velocity is too slow. Use 2"!!!!!!
    Licensed residential and commercial plumber

Similar Threads

  1. Laundry drain pipe help for s-trap location. Canada
    By klrman in forum Canadian Plumbing Code Questions
    Replies: 11
    Last Post: 06-03-2010, 02:40 PM
  2. Laundry drain pipe help for s-trap location, Canada
    By klrman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 06-03-2010, 02:40 PM
  3. Typical drain pipe size for IPC code?
    By Mudball in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 18
    Last Post: 08-24-2009, 06:22 AM
  4. IPC Code: Main line and Venting size
    By construct30 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 12-05-2007, 05:21 PM
  5. Matching pump h.p. to well point size and length?
    By ron in sc in forum Pumps and Tanks Well Forum & Blog
    Replies: 11
    Last Post: 06-06-2007, 05:52 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •