    Default Vent Upstream from Fixture?

    Underground inspection was rejected today because vent for WC on horizontal branch was between fixture and main drain. I was required to move vent upstream from combo to the water closet. I read UPC code to say that vent should be downstream from fixture. Am I missing something?

  2. #2
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Where exactly was the vent? How many feet from the WC? Were there any other fixtures in your setup? Just trying to fully understand what you had and exactly where he wanted the vent.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  3. #3
    Illinois Licensed Plumber SewerRatz's Avatar
    Join Date
    Nov 2008
    Location
    Chicago, IL
    Posts
    1,705

    Default

    Pictures are good and helpful

  4. #4
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    Quote Originally Posted by SewerRatz View Post
    Pictures are good and helpful
    5 words covered my 3 questions and 1 statement.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  5. #5
    DIY Junior Member
    Join Date
    Sep 2009
    Location
    St Louis
    Posts
    2

    Default

    Wish i had pic's. The original vent was 4x2 combo on its back 2or 3 inches downstream of WC combo. Moved just upstream. the next fixture is another 4x2 combo going to shower, it is revented near trap. Next is floor drain 15 feet away and is on 3" pipe and trap. He ok'd everything else but wanted vent moved. Thanks for help!

  6. #6
    Master Plumber-Gas Fitter shacko's Avatar
    Join Date
    Jan 2006
    Location
    Rosedale, Md
    Posts
    561

    Question

    Quote Originally Posted by Raildog View Post
    Underground inspection was rejected today because vent for WC on horizontal branch was between fixture and main drain. I was required to move vent upstream from combo to the water closet. I read UPC code to say that vent should be downstream from fixture. Am I missing something?
    Common practice with most codes is to have the fixture wash the vent, so if your vent was downstream of the toilet I don't know why it was regected unless something else was wrong.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default vent

    Upstream or downstream could change definitions depending on the actual circumstances. We would need a picture or other visual to be sure we are interpreting what you describe accurately.