  1. #1

    Default bathroom ceiling fan

    I have come to a standstill of sorts in my bath remodel, hoping the picture helps to explain the situation. We have decided on a bathroom fan for our project, now the problem is how to run it to the outside. This is a 2 story house, going up won't work, there is a bathroom right above. I thought about doing a wall fan, but not quite what we want. We would like to position the fan in the center of the room, and the shortest run to the outside would be across the ceiling joists. Would it be possible to header these joists off where the red lines are, to the rim joist with joist hangers. I am concerned about weakening the floor because there is already a header put in for the upstairs shower. Would this be chopping up the framing too much, or would it be strong enough? I thought of another option; running the ducting with the floor joists thru the ceiling of another room (suspended ceiling, so not too much of a problem). Its about a 20 foot run, and terminates at the deck ledger board on the second floor. (The duct would then be right under the deck) Is this kosher do you think?
    Attached Images Attached Images  

  2. #2
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by muzz View Post
    Would it be possible to header these joists off where the red lines are, to the rim joist with joist hangers. I am concerned about weakening the floor ...
    Yes, that would not be a good idea.

    If those joists are 2x10s, I would add some 3/4" plywood plates (9x48) on each side then use a 4-1/4" hole saw at the vertical centers of those joists and run your duct between your red lines.

  3. #3

    Default

    unfortunately the joists are only 2x8, so I guess the only way to go is thru the next room and out the back of the house. Do you think there would be a problem with it terminating below the deck?

  4. #4

    Default

    almost forgot, planning on buying a panasonic fan, any recommendations where to buy from? Thinking about buying from Westside Wholesale on the net, not a lot of options for buying where I live.
    Last edited by Terry; 05-18-2010 at 02:29 PM.

  5. #5
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by muzz View Post
    unfortunately the joists are only 2x8, so I guess the only way to go is thru the next room and out the back of the house. Do you think there would be a problem with it terminating below the deck?
    "Outside is outside", I would say. But, others here might know more about that kind of thing.

  6. #6
    In the Trades AZ Contractor's Avatar
    Join Date
    Apr 2007
    Location
    Phoenix, AZ
    Posts
    90

    Exclamation

    Do not attempt to cut into the framing members unless you plan on hiring a structural engineer first so he can design it for you.

  7. #7
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    Don't chop up those joists - you're right, they've already been cut up enough. And how would you attach the header with that pipe in the way?

    20 feet's a bit far. I think you'd need a booster fan... and then you'll still have condensation issues to reckon with.

    I'd say, pitch it 1/4 per foot to the outside, so any condensation drains out... but over 20'... have you got 5" of play? Depends on how low the suspended ceiling is, I suppose.

    Any way to go up, inside a wall of the bathroom above?
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  8. #8

    Default

    Well, at least I know that I can't go out thru the bathroom wall, the 20 foot run looks like the only option. I am hoping to keep the pipe within the joist cavity for the run, but depends on where the outlet is on the fan itself. I have another 3 inches or so below the joists in the next room, so I have some room if I need it. I am thinking that if I use foil tape on all the joints and secure it to the joists with strapping or something along those lines to keep a pitch to the pipe, I should be ok? There is some option of going up, but hate to consider it really--wouldn't I still have a condensation problem that way?

    Any recommendations where to buy online, I am considering Westside Wholesale; anybody used these guys?

  9. #9

    Default

    I've purchased from Westside several times. They are a good outfit.

    Consider that you'll likely need a booster fan if you running that far. Booster fans make noise and are annoying. I don't care how quite the package says it is. In addition you can't bury the fan. I believe it has a transformer attached to it so you're going to need an access hole to service it.

    I'd look for another solution.

    Does the room butt an outside wall?

    Tom

  10. #10

    Default

    Yes, the one side where I originally was going to install the duct is the outside wall. I had considered a wall fan, but that isn't working out.

    The bath is 10 x 13, and I had wanted to mount the fan in the center of the room. I am putting a soffit in over the vanity area (which is on the outside wall), and am now considering putting the fan in that over the vanity. I have 11 inches of space between the first joist and the rim joist, so it would be a very short run to the outside. The soffit is only 6 inches lower than the ceiling, I am thinking is not the best, but pretty close?

    I am thinking I should buy a timer for the fan since it won't be at ceiling height to make sure to get rid of the moisture in the room. I found a panasonic fan that has the measurements I need to fit (FV-15VQ3), but haven't decided if that is the one yet, still weighing the options.

    I think this may be the best way to go...
    Thanks for everyones input so far...

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,412

    Default

    While they can be pricey, I've seen hygrometer based switches...you set the humidity level you want, and it will run until it gets below that.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    I wish we had more HVAC guys here - I can't think of a fan you could do this with - but it'd be ideal if there was a way to mount a grille onto the side of the soffit?

    Either way, I think the 19' reduction in run far outweights being 6" below ceiling height.
    Last edited by frenchie; 11-09-2007 at 07:21 AM.
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  13. #13
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by jadnashua View Post
    While they can be pricey, I've seen hygrometer based switches...you set the humidity level you want, and it will run until it gets below that.
    Here is what I have:

    http://thermostats.idtenergystore.co...it_continue=Go

  14. #14
    DIY Senior Member Hube's Avatar
    Join Date
    Sep 2004
    Location
    Ontario
    Posts
    156

    Default

    Imo,the circumstances involved would indicate that the best and safest way is to install a WALL fan. Exhaust the air to the outside,and make sure there is a "backdraft" louvre installed to prevent any entry of outside air when the fan is not runnining.

    And fyi, there are also soffit vents on the market that incorporate backdraft shutters. They work great too.

  15. #15

    Default

    I think I have decided that I am going to order the panasonic fan, and a dehumidistat as you guys are recommending. The picture shows where I plan on installing the fan--it will be an extremely short run to the outside; this is the rim joist that is circled. From what I have read about humidistats, it sounds like the setting on it has to be changed as the outdoor temp changes, correct? With this short of a run, would it be a problem using an elbow right after the exhaust flange? I am thinking that I would have to put an elbow up, and then out thru the rim joist.