Sewer Lateral Questions/Recommendations

Users who are viewing this thread

TLowing

New Member
Messages
5
Reaction score
0
Points
1
Location
Virginia
I'm building a house and our proposed 4" sewer lateral runs a total of about 550ft. Starting elevation at the house foundation is about 89 ft. After about 100 ft it makes a 90 degree turn then goes for about 450ft. The existing 8 inch manhole is at 76 ft elevation. The County requires clean-outs every 100 ft. Do you have any suggestions or recommendations? With the 1/4" per foot rule, does it always have to slope down or does it apply to just the start and finish elevation over the run?

lateral.png
lateral2.png
 

Reach4

Well-Known Member
Messages
38,931
Reaction score
4,449
Points
113
Location
IL
With the 1/4" per foot rule, does it always have to slope down or does it apply to just the start and finish elevation over the run?
It must slope down continuously.

An 8 inch cleanout would not be called a manhole, I don't think. ;-)
 

Bluebinky

Member
Messages
588
Reaction score
16
Points
18
Location
Des Moines, WA
Not a pro, but here's my take...

The slope should be as uniform as practical, and always a minimum of 2%. You may be required to use 6 inch pipe for such a long run (my AHJ would require it, or possibly even 8 inch which would be a huge royal pain in Washington State with an easement, real manholes and such). One advantage of 6 inch is that you may be able to get away with 1% slope (1/8 inch per foot).

Legally getting into the 100 year floodplain and the creek buffer may be another can of worms.
 