I am new to my home that has city water as well as a non-working well pump. I would like to revive the well to use for irrigation so I started troubleshooting.
It's supplied by 230V on a dedicated double breaker at my main panel. That feeds an isolation switch which then feeds the pressure switch then to the control box and then to the submersible pump.
The control box says it's for a 230V 1/2 HP pump so without pulling the pump I have to assume that it's a 1/2 HP pump.
The pump itself has four wires coming from it to the well-head.
They are yellow, red, black and green.
The yellow, red and black are spliced into the wires going to the control but the green has been cut and taped off. There is no green to the control box.
So far I have established that, since there is no pressure at all in the tank, that the pressure switch is "on" - I have confirmed this by measuring 230V at the control box. The control box had a broken-looking capacitor in it so I have replaced that, like for like.
Since I have limited electrical knowledge I just used a voltage "sniffer" on the wires on the pump side of the splices in the top of the well shaft that I mentioned earlier - voltage is detected when everything is "on".
Is it safe to me assume that everything up until the pump is working correctly and that the pump is what failed, or maybe the 3 wire from the splices to the pump ?
According to the town municipal offices the city water was connected to the home about 6 years ago, presumably because the well failed somehow.
One other test I performed was to hang an amp tester (clamp type) around the three wires running from the control box to the well and when we turned on the isolation switch the current measured exactly 0.00 - it didn't even blink. When we ran that test we didn't know that maybe the numbers cancel each other out and that we should have tested each conductor separately. I no longer have that amp tester as it was borrowed.
So.....
Is there anything else I can do to make a final determination before I pull the pump. I measured the well depth and stopped plumbing when I ran out of line at 250 feet....presumably the pump won't be at the bottom but it could be down 250 feet. Maybe more. My well shaft water level is about 15 feet below grade so hopefully the plumb bob just slid by the well pump about 100 feet down....I'm not usually that lucky :-(
Any advice you can give me would be very much appreciated.
It's supplied by 230V on a dedicated double breaker at my main panel. That feeds an isolation switch which then feeds the pressure switch then to the control box and then to the submersible pump.
The control box says it's for a 230V 1/2 HP pump so without pulling the pump I have to assume that it's a 1/2 HP pump.
The pump itself has four wires coming from it to the well-head.
They are yellow, red, black and green.
The yellow, red and black are spliced into the wires going to the control but the green has been cut and taped off. There is no green to the control box.
So far I have established that, since there is no pressure at all in the tank, that the pressure switch is "on" - I have confirmed this by measuring 230V at the control box. The control box had a broken-looking capacitor in it so I have replaced that, like for like.
Since I have limited electrical knowledge I just used a voltage "sniffer" on the wires on the pump side of the splices in the top of the well shaft that I mentioned earlier - voltage is detected when everything is "on".
Is it safe to me assume that everything up until the pump is working correctly and that the pump is what failed, or maybe the 3 wire from the splices to the pump ?
According to the town municipal offices the city water was connected to the home about 6 years ago, presumably because the well failed somehow.
One other test I performed was to hang an amp tester (clamp type) around the three wires running from the control box to the well and when we turned on the isolation switch the current measured exactly 0.00 - it didn't even blink. When we ran that test we didn't know that maybe the numbers cancel each other out and that we should have tested each conductor separately. I no longer have that amp tester as it was borrowed.
So.....
Is there anything else I can do to make a final determination before I pull the pump. I measured the well depth and stopped plumbing when I ran out of line at 250 feet....presumably the pump won't be at the bottom but it could be down 250 feet. Maybe more. My well shaft water level is about 15 feet below grade so hopefully the plumb bob just slid by the well pump about 100 feet down....I'm not usually that lucky :-(
Any advice you can give me would be very much appreciated.