Hello. Would like to say thanks to this forum as it has been a great resource to me throught the years. Now to my problem.
Had a new well drilled last year, 525'.
Dropped the pump in myself, and has worked good until now. Power went out the other night, water was gone almost immediately, and lots of air when it came back on, I know what that means.
Some background for you guys, pump is a 2hp F&W, sitting at 480', static water level is like 5'. Installed a 8gpm flow reducer right by the well head, and no check valves after lots of reading on here. Have a 40/60 switch and 80 gallon pressure tank. 1" schd 120 pipe in the well also, with a torque arrestor.
So today I went out and played around, obviously lots of water back flowing into well, can here water moving in the lines, and see sediment stirring in my filter. Did some timing exercises.
Pressure tank isolated takes 1.75minutes from 60psi to 40 psi, draining through boiler valve.
Tank and well isolated from house takes 3.5 minutes, no drains open(so that's what the well is losing).
Tank and well isolated from house, it takes 2 minutes to pump up from 40 to 60psi.
Seems to me it must be the pump check valve, if I had a leak that big, it would take much longer to pump up. I do have a fair amount of sediment in my water, could be a contributor, but not even 2 years and I'm gonna have to pull it... that sucks! Last winter could take a shower when the power was out, and still have water!
So, I know it's not a proper solution, but I'm thinking about adding a check valve up top, I'm not pulling this thing and I hate to pay someone to do it, but eventually I know I will have to
Had a new well drilled last year, 525'.
Dropped the pump in myself, and has worked good until now. Power went out the other night, water was gone almost immediately, and lots of air when it came back on, I know what that means.
Some background for you guys, pump is a 2hp F&W, sitting at 480', static water level is like 5'. Installed a 8gpm flow reducer right by the well head, and no check valves after lots of reading on here. Have a 40/60 switch and 80 gallon pressure tank. 1" schd 120 pipe in the well also, with a torque arrestor.
So today I went out and played around, obviously lots of water back flowing into well, can here water moving in the lines, and see sediment stirring in my filter. Did some timing exercises.
Pressure tank isolated takes 1.75minutes from 60psi to 40 psi, draining through boiler valve.
Tank and well isolated from house takes 3.5 minutes, no drains open(so that's what the well is losing).
Tank and well isolated from house, it takes 2 minutes to pump up from 40 to 60psi.
Seems to me it must be the pump check valve, if I had a leak that big, it would take much longer to pump up. I do have a fair amount of sediment in my water, could be a contributor, but not even 2 years and I'm gonna have to pull it... that sucks! Last winter could take a shower when the power was out, and still have water!
So, I know it's not a proper solution, but I'm thinking about adding a check valve up top, I'm not pulling this thing and I hate to pay someone to do it, but eventually I know I will have to