I am with Chris on this one for sure.Chris, that table only applies when branch circuit supplies 2 or more receptacles or outlets.
A duplex receptacle is TWO receptacles.
I am with Chris on this one for sure.Chris, that table only applies when branch circuit supplies 2 or more receptacles or outlets.
I am with Chris on this one for sure.
A duplex receptacle is TWO receptacles.
Ok, I fold. You guys are correct. This is a violation.
I am wrong and I thank you for the lesson.
As I look at the pro panel, I can count a least 35 circuits going into what looks like a 150 ampere 30 circuit panel.(judging by the se cable). I am pretty sure that isn't a 40 or 42 space panel.
Thanks Scott
If you really want a super neat and meet the code and I belive this been show up in one of the electrical magaizne.
Warning Keep your jaws properly supported or get a pillow below it
http://www.electrical-contractor.net/forums/ubbthreads.php/topics/122309/1
Enjoy it.,,
Merci,Marc
Looks nice, I would have used conduit instead.
This has been an outstanding thread. I am the ultimate DIYer. I have learned so much from this site. Thanks Terry. Saying that I would never touch a project I am uncomfortable with. You guys help us all fill in the blanks.
From all the DIYers.... We would love to see more pics and advise on:
Don't do this and why.
You got to see this idea.
Great install/workmanship.
Accident waiting to happen.
Thanks for posting that, Marc. I had those pics bookmarked, a few years ago. Was looking for it the other day, couldn't find it...