Hi
I recently had an L6006C aquastat installed to control the circulation pump for my Biasi cast iron conventional boiler (propane). What would be the best setting for the circ pump to come on and the correct differential? Want boiler protection to prevent condensate but don't want to waste fuel either. The boiler is a cold start and controlled by the house thermostat.
Thanks
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
If it's a gas fired version it's fine to run the circulator at a boiler temp as low as 130-135F without risk of excessive condensation, for an oil burner that should be 140F.

Since the the smallest Biasi cast iron boiler is oversized for the heat load of most homes in Ontario, in most cases it's better to replace the burner's controls with a heat purging economizer control, which will limit the average operating temperature and standby temperature (for lower standby & distribution losses) without short cycling the boiler.
 