CheesecakeLover
New Member
Hi all, I currently have a single 24 V transformer powering 2 Taco zone valves. The transformer is marked as "40 VA", which means it has a current rating of 1.66 Amperes.
The problem is that I believe my Tacos have the older 0.9 A power heads; not the modern 0.3 A heads. If that's true, that means I'm slightly over the capacity of the transformer: 0.9 A * 24 V = 21.6 VA (for 1 valve). Two valves make that 43.2 VA on a 40 VA transformer.
To make things worse, I am about to upgrade one of my thermostats to a digital model, which will of course employ the use of a C wire to allow an additional 20 mA to be drawn from the transformer.
Now that the background is out of the way, I can ask my question: Can't I just use a general-purpose 24 V transformer rated for 2 A? That would be equivalent to a having a "48 VA" power rating. Or am I really better off buying one from a supply house that is specifically meant for zone valves? I honestly can't see any difference, other than the industry-purpose transformers list the power rating in VA.
Even more background: The REASON I would rather purchase a general-purpose transformer is because I can find them with a center-tap (12-0-12). I can utilize that center tap to power a couple voltmeter chips. Doing this will let me keep an eye on the thermostat activity while I'm standing in the boiler room. This helps me diagnose things at a glance, instead of pulling out my multimeter and probing around.
Thank you.
The problem is that I believe my Tacos have the older 0.9 A power heads; not the modern 0.3 A heads. If that's true, that means I'm slightly over the capacity of the transformer: 0.9 A * 24 V = 21.6 VA (for 1 valve). Two valves make that 43.2 VA on a 40 VA transformer.
To make things worse, I am about to upgrade one of my thermostats to a digital model, which will of course employ the use of a C wire to allow an additional 20 mA to be drawn from the transformer.
Now that the background is out of the way, I can ask my question: Can't I just use a general-purpose 24 V transformer rated for 2 A? That would be equivalent to a having a "48 VA" power rating. Or am I really better off buying one from a supply house that is specifically meant for zone valves? I honestly can't see any difference, other than the industry-purpose transformers list the power rating in VA.
Even more background: The REASON I would rather purchase a general-purpose transformer is because I can find them with a center-tap (12-0-12). I can utilize that center tap to power a couple voltmeter chips. Doing this will let me keep an eye on the thermostat activity while I'm standing in the boiler room. This helps me diagnose things at a glance, instead of pulling out my multimeter and probing around.
Thank you.